11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?
Answers were Sorted based on User's Feedback
Answer / shailesh taware
1 CT WITH 3 CORE
1st CORE FOR O/C & E/F PROTECTION
2nd CORE FOR METERING WITH INSULATION CLASS 0.5
3rd CORE FOR DIFFERENTIAL PROTECTION
1 PT WITH 2 CORE
1st CORE FORE O/C & E/F PROTECTION
2nd CORE FORE METERING
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / manjunath kunigal
one set of tertiary winding CT/PT is sufficient for both
metering and protection.
| Is This Answer Correct ? | 11 Yes | 9 No |
Answer / k n naidu
hi,
one three phase set of PTs for both protection & metering
and one three phase set of CTs with two secondary cores one
for metering and protection are required.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mubanga mulenga
You need:
1)Inst., o/c, Metering & EF - 3 CT's
2) REF - 1 CT
3)SBEF - 1 CT
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vikas chauhan
3 no CT (Double core) for 11 kv side for protection and
metering
3 no CT (Double core) for 0.433 kv side for protection and
metering
11/.110 KV 3 phase PT for 11 KV side
secondry side(.433KV side) phase directly connected for
Metering & select relays for .433 KV secondry voltage.
if you select differencial rotection
3 nos CT for Primary and 3 No CT for Secondry side and
interposing CT for Match and neutralise the current in
relay.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / d ramesh
11KV side(delta)
Line side 3core CT :1No. for metering, O/C&E/F protection,
Differential protection with ICT.
0.433KV(Star)
Nuetral CTs :1core for Standby E/F 5p20
Line CTs :3core CT:1No for metering, O/C&E/F
protection,Differential protection with ICT.
1No. 1-core CT in LV nuetral of Transformer of class 5P20
for earth fault protection.
panel side in the panel itself remaining CTs can be
provided for metering, O/C&E/F, and differential cores with
ICT. In both HV panel & LV panel.
| Is This Answer Correct ? | 2 Yes | 1 No |
deisel generators all elcetical calculation formule's
what is meant by dielectric breakdown ? where we using HV test kit & what purpose?
what is meant by switch fuse unit ?
3 Answers Thermal Powertech Corporation India Ltd TPCIL,
Draw SLD feeding from the SS up to distribution board of the load, calculate cable size, breaker sizes, and meter for the following case: Ground Floor: electric room, pump room, 5 shops, each is 15 KW First Floor: 5 shops, each is 15 KW Second Floor: showroom 30 KW Service Loads: water pump 3 KW (3ph) , fire pump 3 KW (3ph), and one DB service 12 KW (3ph).
while we select CT, why the CT ratio is divided by 5?? ex:250/5,15VA,CLASS-1 CT.Why it is divided by 5??Help me please
Can clean earth cable be considered as low current cable
what is hunting?
WE HAVE THE DC RECTIFIER 1500A, INPUT VOLTAGE IS 3 PHASE. HOW TO CALICULATE THE LOAD? 3 PHASE SIDE EITHER dC SIDE. PLEASE SUGGEST ME
Explain why inductance of the iron cored coil changes with current?
What is a difference between indoor transformer and outdoor transformer of same rating
Star Delta Diagram with full description
0 Answers SKS Microfinance, Syscom,
What is meant by rating error prevention in breaker??
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)