How would we calculate the no of earthing pits required for motor /panel..

Answer / syed rafiudeen

18. The GI conductor sizes shall be as listed below.

(1). HT switchgear, structures, cable trays & fence, rails,
gate and steel column
50 X 6 mm

(2). PCC & MCC EARTH PITS
50 X 6 mm

(3). DB
25 X 6 mm

(4). Motor rated above 55 KW & above
50 X 6 mm

(5). Motor rated above 22 KW & up to 55 KW
40 X 6 mm

(6). Motor rated above 5.5KW & up to 55KW
25 X 6 mm






(7). Motor rated up to 5.5 KW
8 SWG. GI wire

(8). Lighting panels & local panel
25 X 6 mm

(9). Control & relay panel
25 X 6 mm

(10). DG frame, excites
50 X 6 mm

(11). DG & TX’mer neutral
50 X 6 mm cu flat

(12). TX’mer body
50 X 6 mm

(13). Push button station
8 SWG. GI wire

(14). Receptacles & welding outlets
8 SWG. GI wire

(15). Lightning Arrestor
25 X 3 mm copper

(16). PLC & WF panels
25 X 3 mm copper

Is This Answer Correct ?    16 Yes 5 No

How would we calculate the no of earthing pits required for motor /panel..

Answer / shreenidhi

There is no general rule to arrive at the exact no of earth
pits.But discharging of leakage current is certainly
dependent on the area/cross section of the material.In
other terms for any equipment the earth strip size is
calculated on the current to be carried by that strip.First
the leakage current/current to be carried is calculated and
the size of the strip is determined/sized.For most of the
electrical equipments like Transformer,DG set etc.,the
general concept is to have 4 nos earth pits.2 nos for body
with 2 seperate strips and the pits shorted and 2 nos for
neutral with 2 seperate strips and the pits shorted.The
general rule is that for neutral ,the strip size should be
capable to carry neutral current of that equipment & for
body the strip should be capable to carry half of neutral
current.For example for 100kVA transformer,the full load
current is around 140A.The strip connected should be
capable to carry atleast 70A(neutral current)which means a
strip of GI 25x3mm should be enough to carry the current
and for body a strip of 25x3 will do the needful.Here I am
taking the strip size that is generally used as
standards.However a strip with lesser size which can carry
a current of 35A can be used for body earthing.The reason
for using 2 earth pits for each body and neutral and then
shorting them is to serve as back up.If one strip gets
corroded and cuts the continuity is broken and the other
leakage current flows throgh the other run thery by
completing the circuit.Similarly for panels the no of pits
should be 2 nos.The size can be decided on the main incomer
breaker.For example if main incomer to breaker is 400A,then
body earthing for panel can have a strip size of 25x6 mm
which can easily carry 100A.

Is This Answer Correct ?    9 Yes 1 No

How would we calculate the no of earthing pits required for motor /panel..

Answer / ramkumar

it depends on the resisitivity of soiland time for fault
current to pass through(1 sec or 3 sec).there is a formula
which gives the area for earthing required.this is is
divided by area of one earth plate.this gives the no of
earthpits required.

Is This Answer Correct ?    15 Yes 8 No

How would we calculate the no of earthing pits required for motor /panel..

Answer / g. janakiraman

no off earth pits are decided by considering the total
fault current to be dissipated to the ground in case of
fault and the current that can be dissipated by each earth
pit.
normally the density of current for GI strip can be roughly
200 amps per squre cam. based on the lenght and dia of the
pipe used the no of pts can be finalised. this has to be
worked out.

Is This Answer Correct ?    4 Yes 0 No

How would we calculate the no of earthing pits required for motor /panel..

Answer / babloo

the no.of earth pits is usually calculated considering the
fault current, for suppose if the short ckt occurs b/w the
2 phases the fault current will be 3times to the normal
current. For example A 55KW motor carrying the current of
80A during normal running , when the short ckt occurs the
fault current has to dissipate through the earth, so the
earth must be around 25 X 3mm strip.

Is This Answer Correct ?    2 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

what is the IEC standard for Power Cable installation in onshore (like in direct buried ground or above groung)

0 Answers   L&T,


WHICH SUPPLY IS BETTER FOR 4 MW LOAD. 1)TO TAKE NEARER AVAILABLE 11 KV SUPPLY OR 2)TO TAKE 33 KV SUPPLY WHICH IS AVAILABLE AT 10 KM DISTANCE BY INVESTING NEARLY 50-60 LACKHS

1 Answers  


y we use neutral,all r told its used to for closed path..k its a just used to closed path,in a transmission line y we put same conductor used n both phase and neutral..if we use less than phase conductor in neutral mean we ll reduce cost its right r wrong..if we use mean any problem occur in transmission line..

0 Answers   ME,


how can i design a APFCR panel? please explain with example..

1 Answers   Milestone, Reliance Jio,


what will happen if we will not use commutater means if we will give dc to the windings in dc motor

1 Answers  






What is the output of 25 kva 11/.4 kv transformer in kw ? Plz generalized it...

3 Answers   NTPC,


Why there is no provision of breaker in between primary of UAT and generator

1 Answers  


how can get electrical "c" licence.i am complited in DEEE.PASSING YEAR OF 1993.WORKING IN PVT COCERN LT LINE.PLEASE ADVISE ME .CELL NO 9994786021

0 Answers  


how ELCB drip when earth and phase touch together?

2 Answers  


If the neutral wire go pass through the core balance current transformer? If yes then why? and no then why?

2 Answers  


What is the difference between Floot charge and Trickle Charge.

1 Answers   Torrent Power,


I'm generating a pulse of 3V with frequency 80Hz (12.5ms time period) and pulse duration 0.125ms and feeding it to a transformer since i want the pulse to get amplified around 60V. At the output amplification s happening but the pulse is changed to a spike, can you tell me what could be the reason? (an ordinary transformer 220V-12V stepdown transformer is reverse connected ie. now it is 12V-220V stepup and voltage amplification happens)

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)