I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
The initial in-rush current is about 3-4 times the normal current when there is stabilizer as it consists of a transformer . If you keep the switch of the MCB pressed with your finger for a short time while switching on the AC ,the MCB may not trip. You can go in for a 30A MCB
Is This Answer Correct ? | 0 Yes | 3 No |
differentional compound gernater used for wielding porpose. why????????//
what is brushless alternator?
Explain types soft starters?
what is the chemical name and formula of refrigarent R-134a.
what is the difference between potential transformer and capacitive voltage transformer?
if AVR fails in D.G set, what will be the effect?
Why inductors are installed in electrical circuits?
What do you mean by an instrument transformer?
Explain UPS
How many types of electric motors are there?
Differentiate between digital phase converter and ordinary phase converter.
How do i perform grounding of star point of Genset (400V) for making connection with step up transformer of DELTA-DELTA (400V to 20KV) ? while Genset itself has its own neutral and grounding bus bar inside genset breaker box whereas we have another neutral and grounding busbar in synchronizing panel next to genset at maximum distance of 6meter, would someone pls advice if we can only perform neutral grounding in synchronizing panel or should we ground neutral on both places inside genset breaker box and synchronizing panel.