Answer / manoj kumar sankaralingam
i)Differential protection
ii)Restricted earth fault protection
iii)Buchholz relay
iv)Oil temperature indicator
v)Winding temperature indicator
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / karthikeyan
Bucholz relay
under voltage relay
over current relay
inverse time current over relay
pressure relay
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / viren89desai@yahoo.co.in
https://library.e.abb.com/public/4381d7d675f760cdc12575550081d599/AG03-5005E_en_Power_transformer_protection.pdf
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod g
Transformer protection
1) protection provided in the transformer are
A) buchholz relay for both main and oltc (ansi no 63)(alarm and trip)
B) winding temperature (wti) 49(alarm and trip)
C) oil temperature (oti) 49 (alarm and trip)
D) explosion vent or prv
e) Magnetic oil level gauge for alarm
f) Fire protection (Mulsifire system)
g) Lightning Arrester provided in both HV and LV
2) High Voltage side Protection
a) differential protection 87 (operate when fault occurs between HT CT and LV CT)
b) REF restricted earth fault 64 for winding protection
c) over flux for higher rating transformer
d) directional over current towards the source side, operate when fault feeding from LV during coupled with other transformer
NOTE: Master trip 86 relay is provided as the above relays are having less current rating output contacts, can not provide sufficient current huge trip coil circuit breaker. also 86 is provided with manual reset
3) Low voltage side Protection
Instantaneous and time delay over current 50
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avinash
Over current and earth fault Protection relay
Differential Protection relay
Restricted earth fault relay
oil temperature alarm & trip
Winding Temperature & trip
oil Level trip
buchhloz relay
oil surge relay
pressure relief device
HT breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imdad husen
IN TRANSFORMER PROTECTION IF HIGH INTERNAL FAULT OCCUR BETWEEN L.V.C.T.AND H.V.C.T. THEN DIFFERENTIAL RELAY SHOULD BE ORATED AND EXTERNAL FAULT OCCUR DIFFERENTIAL RELAY SHOULD NOT ORATED BECAUSE OF ZERO SEQUENCES CURRENT IS ABSENT
IN TRANSFORMER PROTECTION IF EXTERNAL FAULT OCCUR RESTRICTED EARTH FAULT RELAY SHOULD BE OPARTED
| Is This Answer Correct ? | 0 Yes | 1 No |
What is the meager?
when i am going to take trail on a 3ph sq.i/m motor 5.5kw, i observed that RPM of the motor is very low as compared to the rated RPM and also it rotates in clockwise in first ON command,and anticlock wise in second ON command. finally i observed that on phase is no available . but iam not clear about, why the motor is rotates in both directions without any phase interchanging.pls answer to my question.
why SCR use in power plant
Draw a circuit diagram in which if button is open we can use socket and bulb as a series test circit and if button is close than simple we can use socket as any load purpose.
what is the mager value of star motor and delta motor between phase to ground and phase to phase, and minimum how much should be value ?
What is difference between Over Current & Earth Fault protection?
what is diffrence b/w -48vdc and +48vdc ?
3phase cable calculation formula by motor load
what collector is used for 100kmph-120kmph tracion application?
What is an Isolation Xformer? What is the use of it?
how we can adjust for three phase motor cold stall time ,hot stall time and thermal register set up?
How the circuit breaker is selected for Induction motor of 100 kW, 415 volt, 0.85 power factor, 0.95 efficiency ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)