why not maintain Ph 7.0 in Boiler because 7 Ph is not acidic and not basic.
Answers were Sorted based on User's Feedback
Answer / narendra mishra
You have to keep ph slightly more than 7 so that if Ph gets down below 7 then we will have some time to raise it above 7.if we keep it at 7 & when it gets down to 6 then it will immediately become acidic.
Is This Answer Correct ? | 15 Yes | 7 No |
Answer / arun kumar
Least corrosion point pH 8.5-9.5. For Drum type boiler if we use boiler chemical Trisodium phosphate this chemical not react with scale(calcium carbonate) at neutral pH. If boiler pH acidic means corrosion & Silica carryover also takes place
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / er_nillu
According to Le-chatelier's principal the equillibrium of reaction depends up on pressure and tepmperature at which it is going to takes place.Therefore at neutral point of hydrogen ions concentration (which is responsible for pH) shifts from 7 (7 is the value of pH at atmospheric condition) slightly 8 to 8.5. Simillerly it will shift below 7 at temp below atm temp.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / alok bhattacharya
We need to mix scavenger in feed water in order to make it oxygen free which helps boiler from corrosion. Phosphate dozing is primarily done for this purpose and this raises PH value and usually maintained around 9. Moreover phosphate dozing helps to make magnetite layer which inhibit corrosion.
Acidic water is prohibitive in boiler for above reason, i.e.
Ph below 7.
Thanks
Is This Answer Correct ? | 1 Yes | 0 No |
what is the formula for converting mmwc to tph in a dp type transmitter.what is the range in plc(in tph) if dp tx.range from 0 to 5000mmwc.
2 Answers CCC, Korba Power Plant, Shyam Steel, Utkal Alumina International,
how to differentiate between "ALL fuel lost" and "All Flame Lost" in Boiler MFT condition?
procedure of how to generate power in solar plant.
why not maintain Ph 7.0 in Boiler because 7 Ph is not acidic and not basic.
how shall you calculate PLF on the basis of percentage auxillary load factor
What will happen if the Air Preheater is placed before the Economiser?
6 Answers Bhel, KSPL, Tata Power,
In one plant id fan and fd fan are used for boiler. boiler is used to heat water after some days they install one tank to heat water by hot flue gases coming out from boiler and then hot flue gases are used to heat the air coming from fd fan before leaving out from chimney . but hot flue gases are not coming out from id fan what might be the reason?
Why attemperation is required in HRSG in a combined cycle power plant?
What vibration parameters are monitored in a directly coupled single cylinder turbine and generator?
Looking for Bently Nevada surplus 3300/52-01-00-00 Reverse Rotation Monitor , 4 pieces.
What is MFT and when it is acted.
under which situation or why restricted earth fault protection operates in out side its zone that is external fault