what's the different between ELCB, ELR and ELS?
Answer / asif mansoori
All 3 devices are used for protection from Earth Faults.
Earth Leakage Circuit Breaker is used for putting the circuit off in case any residual current passes out of the circuit & the difference is more than the rating of leakage current, e.g. 300mA, the circuit breaker will go off or cause the main circuit breaker to trip. Usually ELCB is comprising of one main circuit breaker and leakage breaker.
Nowadays, MCB+RCCB acts as RCBO or ELCB. If you use RCCB alone, only protection from leakage current is achieved, if you use both MCB & RCCB, then you get protection from both overload, short circuit and leakage.
ELR is earth leakage relay which is available standalone relay with dry contacts for externally tripping the main circuit breaker.
ELS is also type of ELR, but this is sensor & rating of this is lesser than ELR. For smaller leakage currents, ELS is used.
ELCB-Earth Leakage Circuit Breaker
ELR- Earth Leakage Relay
ELS- Earth Leakage Sensor
| Is This Answer Correct ? | 33 Yes | 2 No |
what is form factor
HOW TO SELECT THE COPPER CABLE SIZES OF MOTORS,TRANSFORMERS?
what is magnetizing and demagnetizing current in generator and motor?
Why it need to form a capcitor when it not been in use from three or two year. Plz describe it technically.
In synchronous motor, how the field current is related to armature current..i know its inversely proportional..but concept wise...i was nt clear....pls help me...
why +24 v and -48 v give to BTS? If -48v protect from surge then why we not use -24 v?
We order Dyn 5 distribution transformer to a company. What arrives is Dyn 11. Is it ok to use this transformer. It will be installed alone.
How to know the back up time for a 5KVA UPS which is connected to 15 nos. of computers? Is there any formula for this? pls. tell me.
How is Grounding or Earthing achieved in Planes and Automobiles?
what is mutual induction principle?
This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????
I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase), before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)