Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what's the different between ELCB, ELR and ELS?



what's the different between ELCB, ELR and ELS?..

Answer / asif mansoori

All 3 devices are used for protection from Earth Faults.

Earth Leakage Circuit Breaker is used for putting the circuit off in case any residual current passes out of the circuit & the difference is more than the rating of leakage current, e.g. 300mA, the circuit breaker will go off or cause the main circuit breaker to trip. Usually ELCB is comprising of one main circuit breaker and leakage breaker.
Nowadays, MCB+RCCB acts as RCBO or ELCB. If you use RCCB alone, only protection from leakage current is achieved, if you use both MCB & RCCB, then you get protection from both overload, short circuit and leakage.

ELR is earth leakage relay which is available standalone relay with dry contacts for externally tripping the main circuit breaker.

ELS is also type of ELR, but this is sensor & rating of this is lesser than ELR. For smaller leakage currents, ELS is used.

ELCB-Earth Leakage Circuit Breaker
ELR- Earth Leakage Relay
ELS- Earth Leakage Sensor

Is This Answer Correct ?    33 Yes 2 No

Post New Answer

More Electrical Engineering Interview Questions

what is form factor

2 Answers  


HOW TO SELECT THE COPPER CABLE SIZES OF MOTORS,TRANSFORMERS?

0 Answers   Eastern Produce,


what is magnetizing and demagnetizing current in generator and motor?

0 Answers   HBL Power Systems,


Why it need to form a capcitor when it not been in use from three or two year. Plz describe it technically.

0 Answers  


In synchronous motor, how the field current is related to armature current..i know its inversely proportional..but concept wise...i was nt clear....pls help me...

0 Answers   Siemens,


why +24 v and -48 v give to BTS? If -48v protect from surge then why we not use -24 v?

0 Answers  


We order Dyn 5 distribution transformer to a company. What arrives is Dyn 11. Is it ok to use this transformer. It will be installed alone.

3 Answers   G&S Construction,


How to know the back up time for a 5KVA UPS which is connected to 15 nos. of computers? Is there any formula for this? pls. tell me.

1 Answers   HAL,


How is Grounding or Earthing achieved in Planes and Automobiles?

3 Answers   ABC,


what is mutual induction principle?

2 Answers  


This is about the recent problem that we have faced in our project site. We have 6/7.5 MVA. 66/11kV three phase star - star power transformer. The neutral was solidly connected to the earthing mat. But because of high resistance of earthing mat (130 ohm on LV and 180 ohm on HV), one day LV side neutral earthing conductor melted and we had a huge damage. Can any one plz tell me what might happen when we connect power transformer neutral to the earthing mat which has high resistance (>100 ohm ) ?????

2 Answers  


I have a question, I visit 01 site and face a problem, there is 2.5 ton Air Con working, when air con compressor is running at that time rectifier voltages are increasing upto 290-295 v and rectifier is giving main high alarm (rectifier is APC single phase), before starting compressor rectifier voltages was 230v. when air con is going off rectifier voltages are decreasing smoothly at its actual voltages 230v. Load on Genset phases is this: Red-13.5 amp AC (Air Con load), Yellow-1.7 amp AC (BTS lights etc.) and Blew-4 amp AC (telecom system load), Genset phase to phase and neutral to phase voltages are also ok. These are 10 sites having same system and same rectifier APC brand at every site 02 genset are working but the problem is same at all these 10 sites. What will be the reason behind???

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)