We order Dyn 5 distribution transformer to a company. What arrives is Dyn 11. Is it ok to use this transformer.
It will be installed alone.
Answers were Sorted based on User's Feedback
Answer / bheesham acharya
Dyn11 and Dyn5 both are vector Group b/w phases and neutral....
D is indicate Primary side Delta connection,
y is indicate secondary side Star connection,
N is indicate Neutral and
5 and 11 is just indicate the angle
5 is show 30 degree angle and 11 is show 120 degree angle b/w star phase and in neutral connection
Is This Answer Correct ? | 0 Yes | 0 No |
the grid connection required for a 50 MegaWatt fotovoltaic powerplant is higher or lower than 35kv (high or medium tension)?
Why the voltage n frequency of the incoming generator is kept slightly higher than d grid voltage n frequency while synchronization ?
How will earthing is making for Aeroplane?
why should be the frequency is 50 hz only why not others like 45, 95 56 or anything , why should we maintain the frequency constant if so why it is only 50
I need to calculate the Battery bank back up for below configuration:- UPS - 120 KVA Battery Bank - 200Ah Volt of each cell - 12 V Total No of cell - 34 No's Can you please help me to get the battery back up time for above configuration...? along with formula
give me list of material for wiring of 20hp motor?
Define bibo stability.
Give some differences between open loop and closed loop control systems.
how to select the power contactor in Diffrent AC motors.
what kind of battery is used in laptops
How to connect frequency meter in metering circuit?(single phase and three phase frequency meter)phase to phase or phase to neutral
i need mat lab program to find out the transmission line losses,regulation and losses