phase association of 3PH L&T static CT meter is wrong.
means 1PH & 1 CT connected properly and other 2 voltage and
CT's inter changed. what would be the impact in the reading?
Answers were Sorted based on User's Feedback
Answer / manjunath tc
Phase angle error will come into picture and meter will record slow.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / shankar
Lets us understand this problem by taking load as constant and the incoming supply initially it was RYB in sequence.
let Vr=10<0 Ir=5<-10
Vb=10<-120 Ib=10<-20
Vc=10<-240 Ic=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-140)+VbIbcos(-250).
=41.5 watts.
Now lets us consider Y and B phases were wrongly connected to each other
Vr=10<0 Ir=5<-10
Vy=10<-240 Iy=10<-20
Vb=10<-120 Ib=15<-10
Now the total power is P=VrIrcos(-10)+VyIycos(-240)+VbIbcos(-130).
=3.781 watts
so the energy meter will records less units
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / surendar
if 415 v is appliex at three phase in your situationi f r phase is right it will get
higher vol. and other two get lower vol....right ans should be all the three
sholud b same
Is This Answer Correct ? | 2 Yes | 4 No |
Ht panal kia hota ha?
Can someone explain how does an IDMT relay works.
why in an industry; machine having rated 200 h.p stopped after power factor is maintained above 0.97 lag by control panel in view-of energy saving
In CT,which terminal(s1,s2) need to be grounded?
do we convert single phase line to three phase at minimum cost?
What is the Difference Between choke & ballast
3 Answers ABB, ICS Integrated Computer Solutions,
say a transformer is designed for 33/11kv step down with ratio 0.33 for load 1 mva. if am giving 11kv as a input that same transformer what will happen to its o/p voltage. and whether it can be operated for 500kva
How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
1 Answers Ajanta Pharma, Bhel, Cosmo Films, Suzlon,
Caliculate the Specific Fuel consumption of 320 kva diesel genarator set?
what will happen when a bulb s connected btwn two phases of a three phase delta connected source?
in communication what is the role of elelctrical engineer?
If 22 KV HT line, Current transformer is 25/5 then how to calculate multiplying factor.