Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Pls.could any one Clarify the following with an example.

1.At What condition Close on Rise and Close on Fall
Pressure Switch contacts are used.
2.If Pressure is abnormal as per set pressure,if connecting
Terminal of pressure switch breaks,how the voltage extends
to Relay base.
3.Are these contacts come under fail safe philasaphy.



Pls.could any one Clarify the following with an example. 1.At What condition Close on Rise and Cl..

Answer / carl_ellis

1. At What condition Close on Rise and Close on Fall
Pressure Switch contacts are used.

Close on Rise: the goal is to detect overpressure in normal
operation.
Common to NO is 'made' in the alarm state, logic high state.
Common to NC is open in the alarm state, a logic low state
Common to NC is open in the alarm state, the fail-safe
mode that detects a logic low state.

Close on Fall: the goal is to detect and signal loss of
pressure in normal operation
Common to NO is 'made' in the alarm state.
Common to NC is open in the alarm state
Common to NC is open in the alarm state, the fail-safe
mode that detects a logic low state

2. If Pressure is abnormal as per set pressure, if
connecting Terminal of pressure switch breaks, how the
voltage extends to Relay base.

A pressure switch is wired directly to the wiring terminals
on the microswitch inside the pressure switch. There is no
'relay base' that I'm aware of.

For normal operation (the Common and the NO contact), either
broken wire will leave the electrical circuit in a logic low
state (no voltage).

In normal operation an alarm state is a logic high condition
(the presence of voltage). That means that a broken wire
open circuit can not conduct a voltage, which means that the
circuit will have a logic low state and will fail to detect
an alarm condition.

If the circuit is wired fail-safe (the Common and the NC
contact) a broken wire creates an open circuit that cannot
conduct voltage so the circuit will be in a logic low state
(the absence of voltage) which is the same as an alarm
condition, a logic low state.

3. Are these contacts come under fail safe philasaphy.

Fail Safe is accomplished by

a) wiring to the Normally Open (NO) contacts (Common to NO
is 'made' when there is an absence of pressure) and

b) having the logic solver look for an alarm condition or a
fail condition in the logic low state.

Either the absence of pressure or an alarm state will
produce a logic low, whether the setpoint is set for
close-on-rise or close-on-fall.

Fail-safe pressure switch wiring can not detect failure
conditions like a plugged impulse line or a valve-blocked
impulse line, with the exception of United Electric's ONE
series electronic pressure switch which has plugged port
detection and an I-AM-WORKING signal mode.

Carl Ellis
Measure First

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

What is difference between loop and zone ?

5 Answers   Adgas, Bilt,


What is the Main principle and formula for the steam flow compensation?

2 Answers  


POSSITIVE PULSE IS APPLIED TO AN INVERTER INPUT.THE TIME FROM THE LEADING EDGE OF THE INPUT TO THE LEADING EDGE OF THE OUTPUT IS 10 ns. THE TIME FROM THE TRAILING EDGE OF THE INPUT TO THE TRYLING EDGE OF THE OUTPUT IS 8 ns. WHAT ARE THE VALUES OF tPLH and tPHL?

0 Answers  


Difine flashing , Cavitaion & Noise? how to minimize these effects

3 Answers   L&T,


what is difference between wheatstone bridge, pirani gauge and strain gauge ??? explain its principle and working

4 Answers  


1)why we are using mostly Ultrasonic Flow meters to measure flow, rather than Radar waves? 2)why we are using Ultrasonic waves and Radar waves to measure the Level?

1 Answers   NTPC,


why we use casced loop

6 Answers  


Definition of level

3 Answers  


how u meassure a room temp?in rtd or themo couple?

4 Answers  


What are difference between automatic and manual control system?

5 Answers  


Can we calibrate an actuator?

5 Answers   Siemens,


I have transmitter of range -20 to -5 kpa.if it is possible to zero trim with atmospheric pressure,means HP and lp having no pressure...what will get after zero trim and it is the right way.....plz give me reply ....

3 Answers   KOC,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)