I've just got into my electrical engineering course and I need some help with a question of mine here.
During a site visit, we were shown a main LT panel which has switchgears, ammeters and different kinds of relays and the distribution network from that panel. In the main LT panel I've noted down the current readings as Ir - 163A, Iy - 150A and Ib - 147A. The Line to Line voltage is 415 V at 50 Hz and Line to Neutral voltage is 230V at 50 Hz.
From the above details, how would I calculate the kVA rating of transformer? The primary side voltage of the transformer is 11 kV and the secondary side voltage is 415V and the frequency is 50 Hz.
Answers were Sorted based on User's Feedback
The transformer actual load [apparent power] S=0.23*
(163+150+147)=105.8 kVA.
You may calculate approximately taken the average current
(163+150+147)/3=153.33 A and the formula sqr(3)
*0.415*153.33=110.2 kVA [4% error].
But this is not the rated power. The rated power and the
rated current have to be written on manufacturer rating
plates.
Is This Answer Correct ? | 0 Yes | 1 No |
For a 50MVA (138/69/13.8 KV) transformer, what would be the maximum demand in order not to exceed 80% of its operating capacity.
What is transient Phenomenon?
why America use 60HZ 110V?
In UPS, battery connections if parallel connection given, what will happen?
In case you don't have coal and salt for earthing, how can you achieve good temporary earthing?
1 Answers Focus Energy, NHPC, ONGC,
different between grounding & earthing?
sir i want previous entrance exam papers for written test
how much cuurrent flow through human body effected ????
7 Answers Divis Laboratories, ICSA,
Describe the difference between a microcontroller and a general purpose computer.
Explain Even and Odd signals?
what is the responsibility of C license holder in industry?
what is the prinsiple of dc motor and construction and working ,application of dc motor.