how to syncronize two dg sets
Answers were Sorted based on User's Feedback
Answer / shri..
1) first start the both DG set.
2) Then check Phase sequence R,Y,B
3) check the LL voltage & LN voltage. (both DG voltage
should same)
4) Check The engine RPM (both engine RPM should same)
5) Check The Frequency (both DG Frequency should same)
6) Then close the both breaker.
7) then cross check the voltage,Frequency,RPM
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / santhosh
DG Sets with equal Voltage, Frequence and RPM should be
connected to a single bus with equal polarity and phase
sequence. Both the DG's should be protected with protecting
devices like breakers.
DG's should be operated in such a way that is starting only
one DG should get ON and as the load crosses 75% of the
capacity of DG then the second DG should get ON.
This will help in minimisng the consumption of fuel, Load
sharing and improves the performance of DG.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / satender
you have first of all Start stop the DG's in manual mode ,
then check the voltage biasing and speed biasing by running
it on load ( single unit ) . Then check the phase sequence
of DG's and then give the synchroniizing command
| Is This Answer Correct ? | 2 Yes | 4 No |
132/6.6ππ πππππππππππ πππππππ πππ πππ πππππ πππ πππππππππ. πΈ'ππ πππππππ πππππππππππ ππ 6.6ππ/415π πππ πΈ πππππππ πππππππ ππ ππππ πππππ πππ ππ ππ 13/6.ππ πππππππππππ?? πΈπ π½π.. ππππ π ππ’??
what is the difference between on line & off line UPS
WHY SECONDARY OF CT SHOULD NEVER BE KEPT OPEN CIRCUITED?
diffrence between windings of high tension side and low tension side of transformer
what is the clear formula to calculate cable size for a load
what is different between buchhoz relay and pressure relife devices in transformer
how to syncronize two dg sets
How to configure the drives in PLC, through Profibus commnication. And to how to address it?
how we findout a ignater is faulty or not?
What is a formula to decide the size of the cable of the star delta motor ( From Contactor to the motor 2 runs )
how can you prove that in CE configuration a transistor has 180 degree phase shifted output
Why one side of secondary of transformer is earthed, to supply single conductor of electric traction system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)