what sud u do if u dont get feedback from control valve?
Answer / carl_ellis
There's two kinds of feedback from a control valve:
a) the change of the process variable because the valve
position changes
b) position feedback directly from the positioner to the
controller/control system.
We'll assume that the question is directed at the loss of
position feedback signal from the loop's positioner.
1) Position feedback cards are options on smart
transmitters and need to be initialized after installation.
Has it been initialized?
2) DC power is typically loop power for position feedback.
Is the loop power supply still functioning?
3) Has the position feedback card or its wiring been
disabled or removed?
4) If the position feedback loop is intrinsically safe, is
the loop's I/S barrier open circuited?
5) Has the loop wiring been changed in some manner so as to
affect the position feedback signal integrity?
Carl Ellis
Measure First
Is This Answer Correct ? | 8 Yes | 0 No |
What is the differences of Level swich( LS ) and Level Transmitter(LT)
3element
why we use npn sensor in vibration monitoring system
1- Explain about HPM 2- What is the FSC and explain the configuration of FSC 3- explain the complete loop of vibration, how it works (field to control room) 4- What is the use of proxymitter? 5- During job your partner effected with H2S then what you have to do. 6- what type of gland packing uses when valve glind is leaking.
please send the hpcl (instrumentation) model placement papers to my mail....
9 Answers HPCL, Invensys, IOCL, ONGC,
1. Pl. send details about different types Gas Analyser, like Co2, O2, SOX/NOX, etc. with calibration procedure. 2. How to calibrate H2S gas detector in field?
what is different betwen Process zero and atm zero?
pls tell me whethere flame proof HMI's are available or every HMI is manufactured by considering flame proof standard.
how to calibrate a capillary type level transmitter for a closed tank in field? also what is the procedure for commissioning a capillary level transmitter for a closed tank?
can i calibrate DP transmitter online (while Tx in Service) if yes ,how?
what is meaning of software redundency and hardware redundency?
Single acting ON-OFF valve. it is air to open. when sov energized , valve will be open, so during that if air fail then what will be the condition of valve ( open or close ) ???