WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS "
When the operation Download to HIS message appears:
Equalize start. HIS0163
WARNING: Could not connect to equalize destination. (7001)
Retrying. Number of retries = 0/1
ERROR: LdXopsLoadMain: connect error 10060
ERROR: LdXopsLoadMain: connect error 10060
ERROR: Processing terminated due to connection error. (7002)
Equalization end with errors. HIS0163
---- ERROR = 3 WARNING = 1 ----
Tell me, please, why and how to solve the problem."
Answers were Sorted based on User's Feedback
Answer / jigaranadkat
Dear Prasanth,
Please rest assured that your control network is good you
only have the problem in your open network. Thats the
reason that your plant functionality will not be affcted
but you can not download in to HIS0163.
Please follow the below procedure and let me know the
feedback...
1) Check the IP address of HIS0163. It should be :
172.17.01.63 and subnet mask : 255.255.0.0
2) Check for corruption of ethernet driver : (Right click
on my computer---> Go to device manager---> Check for
ethernet driver corruption).
3) Go to run.... Type CMD and give folling command...
ping 172.17.01.63... You should not face any dropped
package.
4) Go to run and type: \\172.17.01.63 or \\his0163
You should be exposed to common shared folder CS1000
5) Disable firewall in HIS0163.
7001/7002 is the code that your ENG STATION is not able to
find HIS0163 in the network.
* As a default setting, due to some group policy setting ..
Connection with blank password will be denied access. So
try to have a common administrative password for HIS0164
and HIS0163 and for operator USER NAME=CENTUM and PASSWORD=
CENTUM.
You may write your feedback to
anadkat.jigar@gmail.com
Hope this will resolve your problem.
Thanks & Regards,
Jigar Anadkat
Instrument Engineer
IBN RUSHD a SABIC affiliate.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / prashanth
thanks mr Jigar Anadkat
Instrument Engineer
IBN RUSHD a SABIC affiliate.
your suggession really helped
actualy firewall was turned on in HIS0163.
I TURNED OFF the fire wall and gave download,then it got
dowloaded successfully.
thank you
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / karthik
This means that HIS0163 is down and not connected to the
control network. Check Vnet/IP BUS1 and BUS2 connections and
the IP setting.
Once it's rectified , you should find HIS0163 in .SO (System
status overview).
| Is This Answer Correct ? | 2 Yes | 2 No |
Dear Jigar Anadkat / Prashath,
This is the error.
Equalize start. HIS1145
WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1
ERROR: LdXopsLoadMain: connect error 10061
ERROR: Processing terminated due to connection error. (7002)
Equalization end with errors. HIS1145
---- ERROR = 2 WARNING = 1 ----
Regards,
John
| Is This Answer Correct ? | 1 Yes | 1 No |
why do we use 4-20 ma current why cant o-20ma
What are different types of orifice plates?
What are primary elements of measuring pressure?
what is Dry Leg calibration and where is it used
What are the types of valves?
Why we not use 2-20Ma or 1-20Ma
Name some of the common protocol use in automation.
please can anyone tell me in detail, what's mean by open loop and close loop?
please can any one tell me clearly about pid tuning i am confusing about this .how to tune pid easly?
How d.p. Transmitter can be applied to close tank?
How to calibrate and check thermal mass flow meter of Make thermal instrument company inc model 60?
what is weighfeeder
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)