One 15kw motor Why we used star delta feeder?why not used DOL
please explain in details
Answers were Sorted based on User's Feedback
The star delta starter limits the starting current of the
motor by reducing the voltage across each winding. In star
the voltage is equivalent to the phase to neutral of the
power supply. In delta the phase to phase voltage is
applied across the windings.
With a DOL starter the phase to phase voltage is applied
across the windings. The starting current can be in excess
of 7 times the full load current.
The main reason for using star delta starters is that the
power supply system to the motor does not have to support
the high current needed for DOL starting. If the power
supply is not able to supply the current a voltage dip will
occur affecting all other users on the supply.
Is This Answer Correct ? | 11 Yes | 1 No |
We can use dol stater up to 5HP (dol stater can
not control starting current of motor but protect
by them up to 5HP). We have been using dol
staters to lower rating ac motors due to low cost.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / vijendra joglekar
The Main purpose of using starter in motor to limit the
starting current as you know evry starter have there own
limitations i.e rating,inrussh current holding capacity as
you told 15 kw motor cant use DOL starter because of its
limitaions its not with stand motor rated current .
Is This Answer Correct ? | 0 Yes | 8 No |
Is it required to lay 2 runs of GI wires along with armoured cables from one power DB to another Power DB?
i need to calulate the cable size when watts are mentaind wat z the formula
sir What is the different bet'n "Active & passive" sensors
size of condotory fron voltage level
what is recommended breakdown voltage of transformer oil?
What is diversity factor and how to calculate it
2 Answers Al Faraa, Amul, Pentagon, Sobha Developers,
how one can check the Current of a DC 12 V battery ? Procedure. I told that take a thick wire (having more wires in it) and then join the + and - terminals of battery with the help of two ends of a thick wire .... is this correct or wrong .....
Why VL is more than the Vc?
WHY NUTRAL GROUND SYSTEM USED IN 33KV SYSTEM
Are generator action and motor action relates to a particular machine only?
how to calculate transformer load?
We have a bank capacitor rating of 60 KVAR for a overall load of 160 KVA and we have connected three loads of 50KVA each. We would like to auto matically correct PF using APFC. How do we design it?