1 How to calculate dp transmitter
steam and water?
2 impulse line for liquid steam and
gas
Answer / carl_ellis
The DP pressure/flow transmitter is mounted above the pipe
for gas applications (empty impulse tubing).
The DP pressure/flow transmitter is mounted below the pipe
for liquid applications (liquid filled impulse tubing)
Steam flow applications using DP pressure transmitters were
historically mounted below-the-pipe (water filled impulse
tubing, frequently with condensate/seal pots), until
Emerson/Rosemount recently discovered that within certain
temperature limits, a DP transmitter close coupled on a
coplanar manifold to an Annubar averaging pitot tube can
survive steam temperatures mounted above-the-pipe.
See this link for Emerson's white paper on steam service
installation recommendations:
http://www2.emersonprocess.com/siteadmincenter/PM%
20Rosemount%20Documents/00870-0200-4809.pdf
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 0 No |
i have one absolute pressure transmitter for the range is -400mmhg to 400mmhg. If i do the zero trim at atmosphere the transmitter should be give 4ma or 12ma? which one is correct?
what is Best Among SINK Or SOURCE Type Design In Digital Signal, Either Iput Or Output? WHY?Can any one..
Can all intrinsic safe transmitters are provided with inbuilt zener barriers? why
what is Potential free contact? where it is used?
3 Answers Engineers India Limited,
how u measure flow?orifice measurement?why all ft in square root?
where are following valves are applicable to install. can any valve be installed any line. globe valve butterfly valve boll valve gate valve
What is rtd output signal
what is the T/C & RTD mesuremaint?
can we copy the software from a transmitter using hht(hart 275) ?
how is work pressure switch& level switch?what is the principle of this?
What is the difference between HMI,SCADA and MMI,not abbrevation?
i saw in my company drawing seat cable size as mensioned like this 12p*15 sqmm,12t*1.5sqmm, 9c*1.5sqmm. now what my que is what is mean by p , t , c.