How can I make calculation for Install level transmitter
(DP) for open tank and cloes tank?
Answer / mnb
For open tank you just connect HP side to the bottom of the tank and vent LP side to the atmosphere.
Head pressure becomes liquid level .URV=Height*specific gravity (H*SG) and LRV =0.
For closed tank, use dry leg for non condensate liquids and use wet leg for condensate liquids.
Dry leg-connect HP side to bottom and LP side to top of the tank. LRV =0, URV= H*SG.
No need to bother about pressure inside the tank because it acts upon both sides equally.
Wet leg- connect Hp side to lower tapping and LP side to upper tapping and fill the Lp side with process liquid.
LRV=h2*sg
URV= h1*sg-h2*sg.
h1= level of liquid at HP side
h2= level of liquid at LP side.
Is This Answer Correct ? | 1 Yes | 0 No |
please tell me how to convert double acting ytc positioner yt-1200 into single acting ytc positioner ?
re i got gre score of 950,and toefl of 69 is this score sufficient actually my husband is presently in US i need to go please help me
how to do loop checking pls email to shanavaska2000@yahoo.com
Explain plc level and its type?
Ple give me "INDUSTRIAL INSTRUMENTATION AND CONTROL S.k. Singh 3th edition" Solution manual to self-Check Quiz and chapter-wise PowerPoint Slides. Home web-site not available... Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Thanks for all...
What is exact difference between the panel earthing and system earthing in DCS system. What is the value of resistence.
How I identify to solonied coil which is 24v or 230v In our lab.because there is no tag.
1 Answers MRPL Mangalore Refinery and Petrochemicals Limited,
What is minimum distance between three thermocouples (2oo3) mounted on same pipe line (20")? Technically accepted by stright line mounted or circler mounted?
i/p converter always for supply pessure from 3~15 psi only !! And from where this converter bleed the air.
How Honeywell FSC is functioning and what is its purpose? Can we bypasa it and only use DCS instead of that.
Where is the flow transmitter installed with respect to control valve, state reason.
why we are using MARSHALLING PANEL? what is the role?