I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
Answers were Sorted based on User's Feedback
Your tx's range is 0~10000mmwc if u
use it at 0~1000mmwc head press tank
than it will indicate 10% level when tank
full. So just calibrate it (configure it) at
0~1000mmwc before take inservice for
actual reading of tank at output
Is This Answer Correct ? | 17 Yes | 3 No |
Answer / ys
u can use this transmitter. but u should rerange the
transmitter.(ie if tank service is water and ur lt is dry
leg type,then LRV=0 and URV=1000MMH2O.. If ur lt is wet leg
calibrated, then LRV= -1000 AND URV=0 MMH2O)
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
I have a LT of 10000mmwc range. can i use this LT in
1000mmwc range of tank?? if yes than what happened???
A change from a range of 10000 mmwc to 1000 mmwc is a turn
down of 10:1
If your transmitter supports a minimum range of 1000 mmwc
within the accuracy spec you require, then re-range the
transmitter and use it.
Most smart DP transmitters from major manufacturers will
support this.
Carl Ellis
Measure First
Is This Answer Correct ? | 1 Yes | 0 No |
Can any one tell me what type of question asked for instrumentation and control interview panel??? pls mail ramashankar.goel@gmail.com
what is the difference in Kg/cm2 and mmwc?
Can anyone help me with the Question bank(objective type) for complete Instrumentation engineering,either a soft copy or a Hard copy(Book),or the name of the author ,or publisher.
How many types of sensor
what is the exact job for automation enggineer?
is here anybody who knows how to calibrate the pressure transmitter? ONLINE
What is the use of temprature compensation?
For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?
What is the difference between dry contact and wet contact?
How can we calibrate the level interface for Fisher® FIELDVUE® DLC3000?if use water to calibrate and our liquid SG are 0.75 and 1 ,Displacer height=14" and How much should be set SG in trasmitter during calibrate,for URV and LRV how shold be set
WHAT IS DIFFERENCE BETWEEN TWO WIRE RTD AND THREE WIRE RTD?
how to calibrate Necleuonic level transmitter.?