Answer / carl_ellis
Water vapor in a vessel (like a boiler drum) will condense
in piping/tubing attached to the upper tap. The condensed
water collects in the piping/impulse tubing connected to the
transmitters low side port.
The water exerts a pressure on the transmitter's low side
port. If the liquid columns stays at the same height, then
it can assumed to be a constant which can be used as part of
the level calculation.
So boilers use a 'wet leg' where the low side leg is
deliberately filled with fluid and is expected to remain at
a constant level.
A differential pressure level transmitter works by
subtracting the low side from the high side.
DP = high side - low side
In this case, the low side liquid column of water exerts a
pressure of 450 mm wc. wc = water column
When the drum is empty,
the high side measures 0 pressure, 0 mm wc.
the wet leg measures 450 mm wc.
DP = high side minus low side
DP = 0 mm - 450 mm = -450 mm wc
When the drum is full, the high side pressure will be (steam
pressure + 450 mm wc) where the 450 mm wc is the water
column in the drum.
The low side pressure will be (steam pressure + 450 mm wc)
where the 450 mm wc is the water column in the low side
impulse tubing/piping.
DP = high side minus low side
DP = (steam pressure + 450 mm wc) - (steam pressure + 450 mm
wc) = 0 mm wc
So empty = -450 mm wc, full = 0 mm wc.
The transmitter's range is -450 to 0 mm wc.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
what is the difference between auto tuning and manual tuning of controllers(eg:PID,PI,PD CONTROLLERS )
How can I read the electrical drawing easily?
what should be minimum length and size of impulse line for steam flow orifice and feed water orifice? asked by sanjay parihar
plz send me placement paper of ongc
is any standard angle for thermowell mounting for horizontal and vertical pipe lines?
how feedback signal frm rtd can be use for 2 purpose, i.e. 1for local monitoring and 2nd for controlling in dcs.so how many wired RTD can be used
how does we do bench calibration of a differential transmitter.
if tx. dp increase or decrese what happend in the reading
I am using 971 Enraf radar level transmitter for LPG tanks ,the tank side indicator gives the error code 999999999FL can any body give me any diagnostic for this issue?
How to convert 0-2500mmH2o into kg/hr? Or how to convert mmH2O into kg/hr,t/hr etc
Why 250 or 500 ohm load resistance is use in any transmitter
who's take first position in process in the timing of new installation flow transmitter and control vavle. give the answer with logical trick.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)