Why is it that polarization index type test is required for
MV and HV motors and not for LV motors?
Answers were Sorted based on User's Feedback
The polarisation index is used to check the insulation of
MV and HV motors because it is more accurate. Also it
allows a lower voltage than the working voltage of the
motor to be used. In LV motors the megger test is usually
twice the working voltage. If this was used on an 11kv
motor the megger would need to be 22kv.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / cr
As we r letting high current pass through the winding using ht megger,there by improving I.R because the heat produced and the ir ratio for 10 to 1 minute should be around 2.otherwise the insulation can be said to be contaminated with foreign meterial , this check is priority for ht motors
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / prashant
because the moror windig is balance or not and winding of the motor is open or not
Is This Answer Correct ? | 0 Yes | 7 No |
how can synchronous generator can be used as synchronous condenser?
Please nybody say, weather the result of Bharat Oman is declared or not? Probable date of declare???????
What are IP protections used for electrical panels, JB, equipments installed in explosive zones like Petrochemicals, Oil & gas
What is purpose of APFC panel?
7 Answers Techno Electric and Engineering,
We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?
A 60w bulb & a room heater are connected in series.if 60 w bulb is replaced by 100w then what will be the effect on heater out & why?
Why the Petrol Guns in the Petrol bunk are earthed?
only some transformers and some generator requires NGR why?
usually why bettery voltage are 1.5V, even if you open a 9V battery there are six 1.5V batteries in series. is it not possible to increase this voltage other than putting in series
what parameters are should nessary for control technic dc drive(in rolling mills)?
what is the procedure for three phase motor differential relay testing can it do with single phase test kit?
prove that power consumed in 3 phase delta system is 3 times as compared to 3 phase star system