what is the difference between 3 phase 3wire &3phase 4 wire meter?what is the advantage of 3p3w over 3p4w?
Answer / prakash
A 3-phase 3-wire system does not contain a neutral. This
occurs when you have 3-phase loads such as motors that do
not require a neutral. A 3-phase 4-wire system has a
neutral. A neutral is required to obtain either 120 or 277
volts in a 3-phase system. Both of these scenarios can
occur on wye and delta systems.
Is This Answer Correct ? | 10 Yes | 18 No |
What is the voltage violating limit to be considered for load flow study? What is acceptable deviation limit according to relevant standards?
why C.T secondary are rated 5A generally?
If short circuit ratio is high is it bad or good for a machine then tell the reason...
with out name plate details , how to find the metering ct and protection ct.?pls brif explaination about that.
Resistance of low voltage side of transformer compared to high voltage side is A less B equal C more D depens on design
What is the use of Gateway RTU like ABB RTU 560 in power plant, SAS system ?
HOW TO CALCULATE GROUND FAULT CURRENT IN 430V 4000AMP AIR CIRCUIT BREAKER?
what is the formula to calculate the fuel consumption of a diesel generator at different diferent load.
4 Answers Aegis, Network Clothing Company,
Difference between a pilot wire and a normal conductor?
0 Answers United Arab Aluminum Company,
what will happen if earth of 33 kv cable (earthed system) is not connected to earthing pit?
how we calculate the knee point of a protection and metering CT and what is the testing procedure.
we have a 2000kva step down transformer at our site. The HT side is charged from 22000V. So the primary current will be 52.48A. So why the HT breaker(SF6 ABB) is rated of 1250Amps ?