What is Droop Control in Woodward?
Answers were Sorted based on User's Feedback
Principal of droop is to povide stable operation,
Speed droop is a governer function which reduces governer reference speed as load increase.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jerry smith
DROOP in reference to any governor control, is the amount
of allowable "sag" from the desired set point, or speed. A
generator operated by itself and islanded, would be allowed
to be operated with either droop or no droop. The only
exception is that two generating sources are not allowed to
both be at zero droop. Unless their governors are directly
communicating with each other, as in Woodward 2301A systems.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sharanjit
WHEN TWO TURBINES ARE RUNNING IN APLANT IN ISALND MODE THAN ONE IS IN DROOP MODE ANDONE IS MASTER MODE.
AS THEIR ARE GOVERNERS FOR EACH TURBINE. SO WE MAKE ONE GOVERNNER FUNCTIONING AS MASTER EHICH OPERATES AND MAINTAIN ONE TURBINE FUNCTIONING AT A DEFINE DPARAMETER ,BUT THE SECOUND DRROP MODE TURBINE WILL FOLLOW THE MASTER AND WILL FOLLOW LOAD
Is This Answer Correct ? | 0 Yes | 0 No |
How to control cooling tower alge
1 Answers GPL, SPY Agro Industries,
explain why direct on line starting toque and current may not be acceptable
what is turn down ratio
What is LB-SR.
What is the the sequence/logic of burner management system in boilers. What is purging and scavenging?
what's the moog valve
What are the special criteria under which FD fans are switched off during MFT.
If a pump has "N" no .of conections in the discharge. If a connection has a heavy leakage. Then it's motor current get affected or not??
What is the formula for find out the height of chimeny of a powerplant?
2 Answers Rosa Power Supply Company Limited, Sail,
what is the relation between the grid voltage and generator voltage how to link up generator with grid
why high pressure heater will take after sufficient pressure? what happen when high pressure heater will take from COLD REHEAT line at light up time when hp and lp by pass in service.(means can we heater take at low pressure?)
What is tripping relation between the turbine exhaust pressure and turbine last stage pressure....???