how to calibrate displacer type level transmitter by dry
weight method please mention formula for weight calculation
Answer / vikash suthar
here you have not mentioned that displacer is used for single
liquid measurement or Interface level my answer is for single
liquid measurement.
For zero take the weight equal to the weight of the float or
simply hang the float then give the zero
For span take the sp.gravity of the liquid and then take the
volume of the float by pie x r2 x h (r2 is the radius
square)and h is the height of the float.
multiply this sp.gravity and the volume of the float.that
will be the weight of the liquid displace by the float.
Then subtract this weight from the weight of the float that
much weight hang on by replacing the float and give span.
| Is This Answer Correct ? | 14 Yes | 3 No |
how pressure transmitter work, what is its principal to measure and how its generate signal. for pressure transmitterinstallation which precautions must be taken ??
How to zero trim the level transmitter by using foundation fieldbus communicator.
How to calibrate DP transmitter by using HART communicator ?
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
In vortex flow meter how can measure the frequency of vortex generated by vortex flow meter
Why Flow measurement has to use Square Root
why dead weight tester called dead weight tester.
What is force balance principle? State some of its’ advantages.
A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.
What is principle of ultrasonic level transmitter?
Why 1-5 vdc a standard?
1 Answers Process Control Technologies,
What are the interlocks we have to check during the start up of LP/HP compressor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)