Answer / vikash suthar
here you have not mentioned that displacer is used for single
liquid measurement or Interface level my answer is for single
liquid measurement.
For zero take the weight equal to the weight of the float or
simply hang the float then give the zero
For span take the sp.gravity of the liquid and then take the
volume of the float by pie x r2 x h (r2 is the radius
square)and h is the height of the float.
multiply this sp.gravity and the volume of the float.that
will be the weight of the liquid displace by the float.
Then subtract this weight from the weight of the float that
much weight hang on by replacing the float and give span.
Is This Answer Correct ? | 14 Yes | 3 No |
What is cable size for intrenal wiring in DCS or PLC ,from any card to Terminal amd Why
How a conductivity sensor & analyzer work at boiler, whats the principle & science is beyond this,How conductivity sensor sence & convert signal & move toward analyzer & analyzer show reading in percent? also what is temperature compensate option in conductivity analyzer
A RANGE OF TRANSMITTER IS (0-400)B mm abs what is "B"?
How to carry out hot loop checking of closed loop pf temperature control valve & temperature transmitter?
what is absolute pressure and where use in process?
Can anyone explain in a simple way the difference between DCS and PLC?
What will the new flow factor if D/P Transmitter is RE-RANGED from 25" WC to 50" WC
Somebody ask me how many size of control valve what is mean of control valve size?
Explain the difference between mmwc and mmwg?
what is the pressure in the tank when its level of liquid is 1.5 meters when its total capacity is 2 meters
How to Calibrate Interface Level Troll in field
Which tank weighing system is better to install (Accuracy point of view) 1) Tank weighing system with 3 load cell or 2) Tank weighing system with 4 Load cell