The formular of how to calculate a cross sectional cable to feed an electric motor.
Examle: 15KW, 26.1A, 415V. Calculate the cable size in mm2
Answers were Sorted based on User's Feedback
Answer / shridhar awasthi
Since it's an LT cable so in this case we can't apply the min cross sectional formula A=I square root t/K.
to find out the cross sectional area for this case fist find out the Load current which is given 26.01A. so refer the Manufacture cataloge and select the appropriate cable size for full Load current.
after selecting appropriate size of cable we will have to apply the derating factor according to the laying condition.
Now multiply that derating factor to cable ampacity,so we will get actual current carrying capacity of that cable.
Now for find our the no. of runs divide full load current to actual current capacity of cable after applying derating factor,so will get no. of runs.
now calculate voltage drop. if this in the permissible limit the our selection is right and if the V.d. is beyond the the increase the size of cross sectional area or no. of turns.
In this case 4 sqmm copper wire is sufficient for Star-delta starter.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jinesh bhaskaran
we have to consider the type of motor starting, cable length and RPM of the motor.
According to these criteria we can select the cable from the cable manufacturer table.
Is This Answer Correct ? | 0 Yes | 0 No |
what is the equation of converting KW into HP ?
do we use links in a dc circuit?if so what s its use in it?
why commutator is attached with only dc macine
Can anybody tell the formula to calculate temparature rise in the cable with respect to current?
In UPS, battery connections if parallel connection given, what will happen?
In a company the lines carrying 33KV but the load is below 10000Volts so we know that <11KV we can put 11KV lines but the lines are 33KV,..so how we can step down the voltage to 11KV with out erecting a substation
when we r using single phase load and we have power cable of 3.5core with .5 of neutral and neutral is suppose to the returen path of the phase how much current will flow in the neutral.reply.
what is electricial and mechnical interlock.
9 Answers Control Dynamics, EFS, HP,
what is the power factor of an inductive load ? (i) Zero (ii) Lagging (iii) Leading (iv) Unity
How to connect surge arrester with equipment?
Consider three heater bank connected in 3 phase star with neutral.Each heater bank connected in each phase.So each phase get 230 volts supply.my question is,during balance condition, current flow in neutral or Not
How can we calculate the fault level of the distribution system knowing the percentage impedance of transformer & subsequent equipments.