what is the safety of ACB & VCB and how can this work and
how can the service the ACB & VCB parts name with picture
Answers were Sorted based on User's Feedback
As you all knows that all circuit breakers can be called
as on off switch with some safety device ie ACB make and
break contact in air (one moving and one sliding) so it
called air circuit breaker for safety we use in ACB Under
voltage shunt trip closing unit. CBCT for tripping command
relay with over voltage earth fault etc for spring charge
we use motor charging mechanism. Same case with VCB
contacts makes in vacuum to minimize the arc during make
and break contact (one moving and one sliding) on high
voltage other function are same but according to the
voltage rating
Is This Answer Correct ? | 121 Yes | 24 No |
Answer / manny sood
Over voltage
Under voltage
Earth fault
Reverse power
, these are the safety of ACB,
High current
Earth fault
No moisture
, these are the safety of VCB
Is This Answer Correct ? | 91 Yes | 7 No |
Answer / ravi
Reverse power
Under voltage
Over load Current
these are the safety of acb
Is This Answer Correct ? | 73 Yes | 13 No |
Answer / vikash kumar
Under voltage
Over voltage
Earth fault
Ground fault
Closing coil
Triping coil
Shunt coil
Is This Answer Correct ? | 58 Yes | 2 No |
Answer / nadeem khan qadri
Under voltage
Over voltage
Earth fault
Closing coil
Triping coil
Shunt relay
Is This Answer Correct ? | 36 Yes | 3 No |
Answer / lovely surendra singh
Reverse power
Under voltage
Over load Current
single phase preventor
Is This Answer Correct ? | 27 Yes | 4 No |
Answer / kuldeep kumar
Over voltage
Sant relay
Ground fault
Over current
Under voltage
Short circuit
This is vcd safty devies
Is This Answer Correct ? | 4 Yes | 1 No |
why skin effect is decreases with decrease with frequency? why skin effect occur
why the indian frequency is 50 hz & U.S.Frequency of 60 hz
1. which type of transformer connection is preferred in case of power supply transformers? (A) Star/Star (B) Delta/Delta (C) Star/Delta (D) Zig Zag/Star 2. In a power transformer usuall which winding is closer to the core? (A) Primary winding (B) Secondary winding (C) Low Voltage winding (D) High Voltage winding 3. The power factor of a purely inductive load is (A) Zero (B) Lagging (C) Leading (D) Unity.
9 Answers CECRI_Central_Electrical_Research_Institute,
what is the difference in using the 125% and the 250% factor of safety in calculating circuit breakers capacity for motors,which is more reliable to use the 125% or 250%??
How to calculate capacitor bank value to maintain unity power factor with some suitable example?
what is mean by busbar and what is the difference between busbar,transmissionline,feeder,distribution line
what is the highest voltage for transmitting electrical power in india
what happens to a turbo alternator if it get trip and 1 out of 3 poles of circuit breaker in close condition
Can we use a Potential Transformer for Auxilliary Power supply( Spring charge Motor, Lighting etc)?
A 100KVA SINGLE PHASE TRANSFORMER 10000/200V,50HZ REQUIRES 300V AT HV SIDE TO CIRCULATE FULL LOAD CURRENT WITH LV SHORT CIRCUITED.THE INTAKE IS 1000W.THE % OF REGULATION ON FULL LOAD AT 0.8 PF LAGGING WILL BE HOW MUCH AND THE SECONDARY TERMINAL VOLTAGE ON 0.8 PF LEADING WILL BE
what is XLPE type cable
During a temperature rise test of a bus duct, it is fed with 415 volts at 2000 amperes. Why dont we get an electric shock if we touch the bus bars?