Profibus DP is a multi-master system. Would it work on RS-485
4W or not, and justify your answer
Answer / carl_ellis
The Profibus DP specification defines the hardware transport
physical layer as 2 wire RS-485. The communications
protocol and the transport layer are both part of the
Profibus DP specification (the separate 2 wire cable for
24Vdc power supply is not involved with the communications).
Any device that passes Profibus DP certification will
conform to the Profibus DP specification.
Therefore, a 4 wire RS-485 device will not work on a
Profibus DP network because it won't be a Profibus DP
device, it does not meet the Profibus DP spec, which is 2
wire RS-485.
Attempting to operate a 4 wire RS-485 device on a Profibus
DP network will only disrupt Profibus DP communications on
the network.
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 1 No |
How to carry out hot loop checking of closed loop pf temperature control valve & temperature transmitter?
I have transmitter of range -20 to -5 kpa.if it is possible to zero trim with atmospheric pressure,means HP and lp having no pressure...what will get after zero trim and it is the right way.....plz give me reply ....
Types of contol loops
What is voltage regulator?
What is the procedure of changing a Faulty Module of Allen Bradley PlC without stopping the Process
Why Flow measure in Square-root?
Whether the DI, DOs shields can be connected with Analog Input Shield Earthpit?
how can i calibrate a smart temperature transmitter used by druck 720 process calibrator?
how to tune the closed pid loop?
how many maximum enter 2mm Dia solid cylindrical pipe into 8mm Dia hollow cylindrical pipe. give answer with calculation.
what are the possible reasons if a control valve fails to open/close?
Why the industry's standard current standards are from 4mA to 20mA,not from 0mA or any other range?