Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


When a field input to plc is coming from 400 to 600 meters
and the input is in 24 V DC? So signal cable of which cross
section i should select for proper signal to plc?

Answers were Sorted based on User's Feedback



When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal ..

Answer / gaurav kale

you can use 0.5 Sq mm shieled for analog .....Upto 600 m no
problem ....but generally as per standerds above 500m you
will have to go with Fibre optic cable

Is This Answer Correct ?    9 Yes 6 No

When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal ..

Answer / laxit

For this type of circuit, use Relay output instead of
direct driving through the PLC output. As these SOV's are
not the low power wattage, Prefer to use 2.5 Sq.mm as a
general for such digital output.Relay contact shall be
selected accordingly.

Is This Answer Correct ?    0 Yes 0 No

When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal ..

Answer / jayeshpateler

as per the 1cm3 core wire will be find also check the
current require then as per the current if it is higher
than you can carry but if current is low then you need to
use the repeater for that.

Is This Answer Correct ?    4 Yes 5 No

When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal ..

Answer / mwah

yes gaurav kale is right about 0.5 sq.mm twisted pair
shielded cable but u have to install repeater to make sure
theres no degrading of the signal at the end.

Is This Answer Correct ?    2 Yes 3 No

When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal ..

Answer / janes

It is all depends on the Load of the Field Instrument.
After Getting the load apply the Voltahe Drop Formula.
Also the input is 24VDC but define the Amp. is it 20A/ 10A.
that is 24Vdc 10A.

For 24VDC 10A Power supply and the Field Instrument is SOV
with 18 Watts, and the Distance is 600 meter then use the 2
Core 2.5 Sqmm Cable as per below Formula.

% Voltage Drop = Length X Current X R Cos0 + X sign0 /
Number of run X Voltage X 10.

Is This Answer Correct ?    2 Yes 5 No

Post New Answer

More Instrumentation Interview Questions

What is meant by cold float of compressor shaft.

1 Answers   Sabic,


whats diffeence between dcs & scada operation.

3 Answers   Orchid, Reliance,


For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?

2 Answers   NA,


Why the tapping connections are taking above for gas service and below for liquid service?

4 Answers  


What is the electronic transmitter frequency.

1 Answers   CPCL, QAFCO,


what will happen if transmitter wire get shoted?

2 Answers   Sabic,


how to measure level under ground tank ? which type of transmitter very accuracy ?

3 Answers   Biocon,


which type of signal used in instrument?

3 Answers   Emco, Makson, Sail, TATA,


What is the difference between fiber optic cable & Ethernet cable

2 Answers   BEMCO, CCC, Pidilite,


How much flow is passing through 6 inch line? There are no gauge, no any transmitters in line.

3 Answers  


a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?

2 Answers  


plz you help about Que paper of mahagenco previous your,any model paper relad to it{maharastra power genration}

0 Answers   MahaGenco,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)