In 63kva LT Distribution Box Why the outgoing of 63A kit kat
is connected to 200 A link disconnector? as the output of kit
kat is only 63 A?
Answer / k.prakashchandra
The link should be of at least twice the rating of fuses, as
otherwise you will have to replace links instead of fuses.