how to select earthing conductor size of amy motor/panel
etc.
Answer / k
use IS 3043
earthing cond size in sq mm S = A * sqrt(t)/k
A = fault current in amps
k = factor given in IS
refer website : www.jptechnosoft.com
| Is This Answer Correct ? | 16 Yes | 7 No |