we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / shariff

It can be step down from 66kV to 440V,but the problem is
above 33kV power transformers will be in treated as EHV,
and normally they will carry loads in terms 20 or 12.5MVA
etc. then for e.g for 20MVA the sec. current with 440V will
be 20x10E6/440=45kA( Normal rating), where this power
transformer cant be made practically with huge cuurent. So
practically we will go for 66kV to 11kV normally, where
Current is the limiting factor...

Is This Answer Correct ?    32 Yes 4 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / k.prakashchandra

Inside a factory it is feasible.But for public utility you
can not erect regular 66KV/433V substations say ,every 500
meters, as long LT distribution lines can not drawn in view
of current and voltage drop.

Is This Answer Correct ?    11 Yes 3 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / yogender goel

It increases the power transmission cost very high.

Is This Answer Correct ?    8 Yes 2 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / jaheerabbas

if we are converting the 33Kv to 440v directly, wastage of
power is more in the form of heat,so that we required large
no of heat sink too....heat sink cost will be more compare
to transformer, so that we go for the step by step convertion

Is This Answer Correct ?    14 Yes 10 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / lakesh thakur

when we convert 66kv to 440v directly then transformer size
will increase & loses will also increase. So we should
increase the size of heat sinke. So directly we can say the
cost of whole our project will increase & also increase MVA
rating

Is This Answer Correct ?    3 Yes 0 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / ved prakash

Basic insulation level at HV & LV side is also a big factor.

Is This Answer Correct ?    1 Yes 0 No

we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why not we convert directly from 66kv to440..

Answer / ramki

fulls , there is mutual coupling in between the windings , so for 66/33/11/133..like this we can found the mutual coupling as a nearly 1.......so wethis

Is This Answer Correct ?    2 Yes 11 No

Post New Answer

More Electrical Engineering Interview Questions

In my power station 220 volts dc battery set. they coneected 84th cell taped

1 Answers   KPTCL,


Write the analogous electrical elements in force current analogy for the elements of mechanical translational system.

0 Answers  


what is Ith current?

4 Answers  


What is power factof?

21 Answers   RRB,


why generation is done in delta nad transmission in star? brief

3 Answers  






How the line trap works in substation...?

2 Answers  


Comparision of Air break circuit breaker, SF6 Circuit breaker and vacuum circuit breaker.

0 Answers   Reliance,


What is the main function of fuse?

7 Answers  


Why in earthing, the earthing plate is put in vertical position? and further what is soft coke that is used in earthing?

3 Answers   Wipro,


where solid grounding and where grounding through ngr done and why?

0 Answers   NTPC,


how current is reverse from its normal direction during the fault?

0 Answers   HGF,


My question is abt backlog.I had dropped one subject in my second year, and completed this subject in the 3rd attempt, so how many backlogs i have got?1 or 3?plz sujjest the answer as soon as possible

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)