we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why
not we convert directly from 66kv to440v?
Answers were Sorted based on User's Feedback
Answer / shariff
It can be step down from 66kV to 440V,but the problem is
above 33kV power transformers will be in treated as EHV,
and normally they will carry loads in terms 20 or 12.5MVA
etc. then for e.g for 20MVA the sec. current with 440V will
be 20x10E6/440=45kA( Normal rating), where this power
transformer cant be made practically with huge cuurent. So
practically we will go for 66kV to 11kV normally, where
Current is the limiting factor...
| Is This Answer Correct ? | 32 Yes | 4 No |
Answer / k.prakashchandra
Inside a factory it is feasible.But for public utility you
can not erect regular 66KV/433V substations say ,every 500
meters, as long LT distribution lines can not drawn in view
of current and voltage drop.
| Is This Answer Correct ? | 11 Yes | 3 No |
It increases the power transmission cost very high.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / jaheerabbas
if we are converting the 33Kv to 440v directly, wastage of
power is more in the form of heat,so that we required large
no of heat sink too....heat sink cost will be more compare
to transformer, so that we go for the step by step convertion
| Is This Answer Correct ? | 14 Yes | 10 No |
Answer / lakesh thakur
when we convert 66kv to 440v directly then transformer size
will increase & loses will also increase. So we should
increase the size of heat sinke. So directly we can say the
cost of whole our project will increase & also increase MVA
rating
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ved prakash
Basic insulation level at HV & LV side is also a big factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ramki
fulls , there is mutual coupling in between the windings , so for 66/33/11/133..like this we can found the mutual coupling as a nearly 1.......so wethis
| Is This Answer Correct ? | 2 Yes | 11 No |
how can u determine size of the conductor by knowing the voltage level
How to calculate the efficiency of Turbo Generator(Alternator) in general....?
what is principle in relay testing kit?
Dear sir/mam Iwant complete details of Naintenence of 33kv/433v Transformer having 1250 KVa
why electron not flow in open loop,how they know path is open ?
Re: can you give main difference between ELCB 2pole And RCCB 2pole? And how this devices operated?
how to find the capacitance value of the motor while running??
Name two low frequency oscillators?
3 phase Motor will be given 2 phase after 2 to 5 second we given 3rd phase so Motor Run sum-time in forward or sum time run reverse direction. All time phase sequence is not change. Why motor run in reverse direction? Please Explain........
In india the power supply is always in multiple of 11, eg.220 V, 440 V... what is the reason?
11 Answers BSES, Electrical, L&T, PSIT,
what is mean by PID & Principal of working
what is the minimum recommended leakage current of an earthed cable connected to the body or skid of an alternator
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)