how to calibrate bubbler type level transmitter of
rosemount make and how to set air flow according to the
range.. give one calibration procedure with one example
A bubbler system uses a pneumatic differential relay as a constant flow regulator. Most bubbler systems include a variable area flowmeter, a rotameter, to indicate the air/gas flow rate and a needle valve for adjusting the flowrate.
Typical air/gas flowrates for bubblers are 8-30 cc/s (1 to 4 SCFH), a flow rate suitable to create a constant stream of bubbles from the dip tube.
The only 'calibration' of the pressure transmitter in a bubbler system is setting the range of the transmitter's 4-20mA output with a zero-to-span range that takes into account the maximum liquid column head pressure that the transmitter will 'see', which takes into account the specific gravity of the liquid.
Conversion to physical level units (accounting for specific gravity) is done in the receiver (indicator/PLC/DCS/PAC/controller).
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 2 No |
DEAR SIR/MADAM MY NAME IS ARKAPROVA BHATTACHARYYA.I AM A FRESHER INSTRUMENTATION ENGINEER.CAN YOU PLEASE SEND SOME QUESTION PAPERS OF GRADUATE ENGINEER TRAINEE EXAM OF DVC(DAMODAR VALLY CORPORATION).MY EMAIL IDs ARE arka_aec@rediffmail.com.
You are looking at the RS-485-side of an RS-232/RS-485 converter and the power supply voltage for the converter is +5V. Under idle conditions (no transmission), and assuming you have enabled the RS-485 output: what would you expect at: (a) Output A measured against output B (b) Output A measured against ground (c) Output B measured against ground
WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HIS message appears: Equalize start. HIS0163 WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. HIS0163 ---- ERROR = 3 WARNING = 1 ---- Tell me, please, why and how to solve the problem."
6 Answers Khas Pvt Ltd, Yokogawa,
we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?
If the average power during generation is zero, why do the analog meters have + and - ?
what is interlock system and why we use of this?
What is Electrical Runout & Mechanical Runout in Vibration measurement.
what should be distance from tapping point to inallation place of instruments?
3 Answers Tasnee Petrochemicals,
HOW TO CALIBRATE A PRESSURE SWITCH?
How we can check the 2 wire proxy switch? & how it is connected to DI MODULE OF PLC?
How Many Slave Can be used in one slave ?
What is instrumentation amplifier?