What are the problems faced while testing HART instruments?
Answer / carl_ellis
Failure to connect with HART can be a laundry list of
issues, the most common of which is the
lack of minimum 230 ohm resistance in the loop.
Other reasons can be
- HART probes connected across the DC power supply, not in
the loop
- failed DC power supply
- electrically noisy DC power supply
- HART modem lacks installed PC driver or internal setup
(serial modems were touchy)
- HART device not at expected HART address (address zero for
point-to-point comm)
- device does not have HART option or HART option has been
disabled.
- HART option replaced by different fieldbus comm card (it's
happened! !)
- Connecting across the test terminals on a pressure
transmitter where there's no HART signal
- HART communicator is dysfunctional or its batteries are
discharged
- lack of DD in communicator/program limits access to the
common commands
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
What is the diffirence between Earth and Neutral and What is the required normal voltage between earth and neutral
Can anybody tell me application of PLC,DCS,SCADA.
What is the difference between fiber optic cable & Ethernet cable
2 Answers BEMCO, CCC, Pidilite,
how can i calibrate E & h make conductivity transmiter . unit : mocro siemens Range :0 to 100 micro siemens sensor : capacitive type
what is differential pressure transmitter and transducer? how to work?
What inherent design and operating principles are included in a modern control system to use predictive maintenance practices to increase overall system reliability?
what is sequence table in DCS . make a logic in sequence table for tripping of ID fan in Boiler(in YOKOGAWA CS 3000 DCS).
defffrence between instruments and instrumentation
typical loop drawing of a simple feedback control comprising of one transmitter and one control
what is maximum vaccume?
When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal cable of which cross section i should select for proper signal to plc?
Why 4mA-20mA current loop selected as standard ???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)