The philosophy for modbus and profibus is same.....the
difference is
1.modbus you can go up to 1200m only in the case of profibus
you can go up to 2-5 km.
2.In modbus the speed will be 125kbs where profibus it will
be 1.5 mbs to 12mbs.
3.In modbus you can connect maximum 32 devices for RS485
where in Profibus you can go upto 127devies without repeater.
| Is This Answer Correct ? | 18 Yes | 4 No |
what is the principle of vibration
how manys ways dp transmitter can be calibrated having range of -150 to 400mmwc,what side pressure u will apply?
how to define the P,I,D value in tuning pid loops in online.
transmitter in 3 connection +,-,And test mode so how Use To Test Mode
what is differences between singal acting and double action valve
1 Answers Carlo Gavazzi, Welspun,
What is the difference between a PLC (Programmable logic controller) and DCS (distributed control system)?
the square root type transmitter r used to which applications
how we can calibrate level transmiiter in field?
what is the principle of ultrasonic flowmwter and radar type flowmeter?
1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling
describe yourself?
how to draw a flowchart for swapping two numbers using bit wise operators?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)