Can a Differential Pressure Transmitter be used as a normal
pressure transmitter??
Answers were Sorted based on User's Feedback
Answer / sarath
yes..you can use DPT as PT by keeping LP line open to atmosphere.connect the supply in HP line.
Is This Answer Correct ? | 49 Yes | 1 No |
Answer / uttam dutta
Normally differential pressure switch have low range, If
the max. pressure of the line is more than the max. range
of pressure switch and if pressure of high pressure line
crosses the limit of diff. pressure switch then the diff.
pressure switch will be damaged and could not be used.
By opening the low line of diff. pressure switch it can be
use to measure the pressure theoretically but practically
it is not used, more over sufficient precaution to be taken
before connecting the high pressure line to the diff.
pressure switch, and this thing is mentioned with each
diff. pressure switch catalog.
Is This Answer Correct ? | 1 Yes | 0 No |
why cant we use mV instead of mA?
12 Answers ABB, Power Grid, Qatar Gas, USW, Visa Steel,
If i want use the 6 kg/cm2 pressure gauge then how to calculate its pressure gauge range?
Explain the difference between mmwc and mmwg?
What is the standard height for stancion supports?
Explain, and give a real-world example of MODULATING control
What is the GK Value in Flowmeter?
wht is Zero Elevation and Zero Suppression?
If boiler drum level transmitter is not working properly what you will do for resolving the problem in plant running condition?
I saw one P&ID 6" control valve has been connected with 8" process line, and 2" valve also connected in parallel with 6" valve. why the 2" valve connected in parallel, Is there any technical reason. please clarify. With Regards-Kittu
WHAT PRINCIPLE OF GAS ANALYSER( CO,CO2,N2)
What is the formula to know the error of weighfeeder after having drop test.
what is unit and element of viberation?