how much resistence in proper earthing?
Answers were Sorted based on User's Feedback
Answer / sureshbabu
for the grid connected system the earthing value must be
below the limit of 1 ohm
for the individual connected system the earthing value must
be less than 5 ohms
this is the IEC standard for earthing and bonding
| Is This Answer Correct ? | 21 Yes | 1 No |
Answer / k.prakashchandra
In case of stations ,the maximum recommended values are
33KV-5 ohm, 66 KV -2, 110 to 400- 1.0 and generating station
-0.5.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / mohan babu bommu
there is no hard and fast rule in large sub stations 1ohm small substatioms 2ohms ither places up 6ohms permissable
| Is This Answer Correct ? | 0 Yes | 0 No |
define as synchronous generator
how earth resistance can be improved in dry soil
how to convert psi into kilo pascal? what is the suction pressure & discharge pressure of chiller?
how to get more than 1000 ohms between 2 earth pits ?
what is the meaning of WYE and DELTA in Electric meter?
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
Which power will flow first if we switch on a motor Active or Reactive? How?
in a plug point why the hole size at the top is large?
It is desired to flood light the front of a building 42 meters wide and 16 meters hig.Projectors of 30 degree beam spread and 1000 watt lamps giving 20 lumen/watt are availabl.If the desired level of illumination is 75 lumen/m and show a suitable scheme.Assume the cofficient of utilization, deprecitation factor and waste light factor are 0.4, 13 and 1.2 respectively.
what is the best way to start a 15 KW motor for pump star-delta or direct on line ? and from how many KW i must use direct on line ?
AC covered area by ton calculation
why most of junction box vendors providing T5/T6 Temp class jb's for T3 area any special reason?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)