if the power factor is .88 i want to increase the power
factor to .99 what number of capacitor is to add?
Answers were Sorted based on User's Feedback
The kVAR of capacitors necessary to raise the power factor to
0.99 from 0.88 is found by using formula referenced above:
0.398 x 50 kW = 20kVAR
this also depends on at what load are we used
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / lemming
pf = P/S
You do not have enough information in your question.
Typically power factor correction questions start with power
and power factor.
| Is This Answer Correct ? | 2 Yes | 2 No |
what work will do diffrential realay DG set
0 Answers IG Petrochemicals Ltd,
How a ship getting grounded
why we have to particulary use ACB for below ratings,even available of MCB,MCCB with that range ?
Find defination of KVA convert in to KW.
25 kva 3 phase dg how many current will take per phase , plssssssss reply me
Caliculate the Specific Fuel consumption of 320 kva diesel genarator set?
How to measure the earth resistance value in a concrete pavement(flood light area)?
How to find Cable size? Caterpillar generator produce (Two generators) 127*2=254 amp at 11 kv . What would be the cable size (XLPE) to supply 256 amp at 11 kv? Air or surrounding Temperature is 32 degree C. Cable will go under ground at 2.5 feet depth. Group Rating Factors is 3 cables. Clearance between cables is 7 cm. Soil Temperature (Ambient) 28o C Soil Thermal Resistivity is 1.2 K.m/W I would like to use 3 separate single core instead of using 3 core cable. Some says I should use three separate single core 120RM cables. Some says 70RM .some says 95. I m totally confused. Is there ant specific rule to determine cable size? What would be the LT cable size to flow 500 Amp current? Ifte My e mail address is ifte13@yahoo.com Anyone please send me the answer to my e mail address, i will be very glad.
dg started in plc mode and load taken later one battery terminal connection will be disconnected by loose connection what will happen for dg and shall we connect battery terminals while dg in load time?
if AVR fails in alternator. what will be the effect.
When lag/lead/lag-lead compensation is employed?
How to calculate the sag on transmission Lines.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)