400kw, 3.3Kv motor want to fix 1000km away from substation.
What is full load current? and what is the cable size for
motor? I amp expecting answer and advice from your side..
thanks...
Answers were Sorted based on User's Feedback
Answer / pillay
i agree with mr prakash,1000KM is a riduculous distance for
practical 400 kw load. any way the usual power formulas will
give you the full load current , the type of starting will
give you an idea of the initial current and the cable
formulas will
guide you about the voltage drops along the distance.Than you
can pick the correct cable size and the cost, may be you
would decide to built a power station.
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.prakashchandra
Only 3.3 KV and 1000KM long line?Drop the idea and have a
mini gen station in the vicinity of the load.
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / j.senthil kumar
Kindly confirm the application of motor, whether does it
require Drive?
If yes, you can add some external AC Choke to avoid the the
loss of power transmission.
Is This Answer Correct ? | 0 Yes | 0 No |
Why thwe Direction of Rotation of a TABLE Fan & CEILING Fan are different?
What is the difference between an ELCB and a RCD?
What is mean by powerfactor. What is the difference between leading and lagging power factor?
what is ht breaker
why normally Generator rating are between 11Kv to 22Kv?
why autotransformers are not safe for supplying low voltage from a high voltage source?
i have 500 amp inductive load of motors ,,,pleas tell me how can i calculate for capacitor bank for improving my power factor to 99 .....calcullations for capacitor bank,,,,
what is RNG in the DG synchronizing by PLC?
What products have you designed which have entered high volume production?
what is mean by derating factor?
why we use ac as a electric appliance in home or daily use?
What is the PI test stand for transformer and what is the producer to do this test?