Answer / hiren
dp transmitter is used to measure DP but the pressure
applied across diaphargm is actual process pressure. so if
any one get fail then transmitter should not fail.
Is This Answer Correct ? | 10 Yes | 1 No |
Answer / komal
Static Pressure is done on DP transmitter because of check
if the transmitter can withstand the static pressure acting
due to Line Pressure when in process. The Line pressure can
be 100 bar but the DP that is measured on transmiter can be
as small as 1000 MM H2O.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / mhakave rajesh
it's span of measurement may be less eg 0- 5 bar,but
pressure acting on single side either of hp or lp (i.e.
process side pressure) may be high, so to check zero of tx
at such operating pressure it is........ so and so.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / b.s.m.raju
This is DP transmeter high static preesure of 100 bar.
Small range will be used 10 mbar. but span range very low
Accuracy will be poor.
Is This Answer Correct ? | 1 Yes | 2 No |
which type of filter gives the constant phase characteristics?
Actual using of tube bender to bend 2 opposite 90 deg at correct measurement center to center of tubing.
Explain why use mmwc unit?
1. What is the main differences between GE Mark IV and Mark V Turbine Control System? 2. what is the main differences between GE Mark V and Mark VI?
How to do gas analysers calibration in AUTO and Manually by using zero and span gas?
how many types of elements are there?
How to convert mA into Percentage?
how level can be measured in open tank with reference to pressure
What is difference between reset and initialization in system.
difference b\w a transducer and a sensor
Instrumentation Safe Guarding test. How to determine the interval time of the test. eg:Halfyearly,Every year,Every three years etc.
Is SmartPlant Instrumentation taking advantage of the quality assurance procedures within Intergraph?