how u calculate ai/di/ao/do capacity in ur dcs?
Answer / malik shams-ul-arfeen
In DCS, we have I/o modules for making DCS I/O function
either analogue or digital, and can be increase or decrease
the capacity of I/Os through installation or de-
installation of I/O module in the rack (MMU).
In bailey INFI-90, each I/O module has 16 chennels (8 for
chenel - A, and 8 for chenel - B).
So, you can calculate the total I/O capacity in DCS by
counting total installed I/O module and multiply them with
16.
PLUS.
Count those I/Os which is provided by the vendor in CIS
(Control and indications) modules.
for more detail, you can contact me
at "msaarfeen@hotmail.com".
Is This Answer Correct ? | 6 Yes | 0 No |
what is a device net.
Where should we terminate the shield and why?
GIVE THE TEMPERATURE RANGE OF PLATIUM RESISTANCE THERMOMETER.
what is the diffrence between LCN and UCN
I want to measure flow by using DP Tx and range is 0 to 1200 Kg/cm2 ?
POSSITIVE PULSE IS APPLIED TO AN INVERTER INPUT.THE TIME FROM THE LEADING EDGE OF THE INPUT TO THE LEADING EDGE OF THE OUTPUT IS 10 ns. THE TIME FROM THE TRAILING EDGE OF THE INPUT TO THE TRYLING EDGE OF THE OUTPUT IS 8 ns. WHAT ARE THE VALUES OF tPLH and tPHL?
What are the Components of Siemens S7 300 Series PLC system ?
What are the maximum packet size of: a) HART b) Profibus DP c)Profibus PA d) DeviceNet e) Foundation Fieldbus
wich is coming the first HAZOP OR SIL
What is the Difference between PE,IE and ISE
how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp side?
we re giviang 24v supply to transmitter and we getting output from tx?now my question is wht we call this complete proces?