how to install the Ph and Conductivity analyser? is there
are any procedures which has to be maintained.
Answers were Sorted based on User's Feedback
Answer / rithesh
in horizontal or vertical pipe while installing we have to
take care about that it should be right angle to
pipe .there should be clearence of angle from sensor part
as specified by vender recomdetion.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / vikash (ineos abs)
Also,take care that it should install in such a way
thatit's glass bulb should always remain wet.
it is very important.
Also exact infrnt of the the sensor at opposit side you can
provide spary assemly to clean the bulb regularly without
removing it.
Is This Answer Correct ? | 1 Yes | 0 No |
What is require for PLC Programming?
what is droop mode n frequency mode in wood ward governor?
Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?
Why plc require in analog input 4-20amp & 0-10 volt?
what type problems create in radar level transmeter and what is its solution
What is the difference between HMI,SCADA and MMI,not abbrevation?
why we are giving negative supply for vibration sensors?
How will you calibrate an interface level trol/normal level trol in line and in w/s?
sir ,iam in dem urgent need of HPCL Paper of Instrumentation Branch plz send me at your earliest convenience at ujjwal_sharma1983@yahoo.com
Draw a 3 element level control loop and explain
A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.
define optical temperature detector