dear friends,
we are use 130 hp load run with 0.98 power factor ( 38KVAR
capacitor connected ). if we need improve the the power
factor to 1 (unity). how much kvar capacitor to be add. have
any formula? please share with me.
Answers were Sorted based on User's Feedback
Answer / jitendra
130*746=96.98kw
kvar=kw(tan pi1-tan pi2)
kvar=96.98(.2030-0)
= 19.68 Kvar
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / bmk mughal
KW=96.98
COS-1.98=11.470
TAN11.470=KVAR1/KW
KVAR1=19.69
COS-11=00
TANO0=KVAR2/KW
KVAR2=0
Required KVAR=KVAR1-KVAR2
=19.69KVAR
Is This Answer Correct ? | 1 Yes | 0 No |
if u can get P.F= 1 u will get noble prize
Is This Answer Correct ? | 0 Yes | 1 No |
what is the dedicated neutral earth in ups? y its required?
If the primary side current of 33/11 transformer is 64 amps then what will be secondary side current?
why the auxilary(starting)winding is provided in single phase inductoin motor?
Dear all, Can anybody tell me that how to choose CT for a specific load? I have a 200kw induction motor, which ratio CT should be installed? Is there a formula or calculation that determines the CT ratio for a load? Regards.
why using 3 phase
Can we perform parallel operation of two transformers when one transformer on load?
what is the effect if we add capacitor on DG supply, it has any loss or benefit.
what are the various parts of airconditioning system used in train and its working
what is recommended breakdown voltage of transformer oil?
what is intermediate switch
how to size a diesel generator set?
how many wires need to be bring to the motor if its star delta starter