what need of NGR(neutral grounding registor)? What it works?
Answers were Sorted based on User's Feedback
NGR used for limiting the ground fault cuurent that is
installed in between generator neutral point and earth in
case of fault that limit the fault current that is of
diffrent type resiatance type, reactance ,petrson coil
earthing. In case of one phase fault that NGR limit the
current and relays detect that and trips the generator.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sivashanmugam
neutral grounding resistor as like that of an earth ... in
generating station most probably transformer is an star to
delta connection generator side delta to star connection i
the transformer side grounding is not possible in case of
that ... one earthing transformer will be palced its an
zigzag winding for grounding the transformer side earth
bcos its an delta conn ... for neutral grounding resistor
ter will be an ngr panel in generator side unequal of
currents in phases grounded in ngr .... am not sure in this
answer if u peoples refer further mail me thank you.....
Is This Answer Correct ? | 2 Yes | 3 No |
in trains i have seen the terminal which is connected at the top of the train is positive .where is negative ? track? i dont think so
what is the function of Droop CT and where it is used?
Why field rheostat is kept in minimum position?
What is the difference between UPS & inverter ? which UPS is better and whos got the edge ? what is the difference between & inverter ? which UPS is better and whos got the edge 12 V , 24 V , 36 V etc what are the advantages of 12 V, 24 V , 36 V etc and what are the disadvantages of 12 V, 24 V, 36 V etc thanks
What is the power ratio between power in Star and Delta circuit?
what is the meaning of stub protection?
why the crow do not feel the current in overhead line when it sits on the wire??????
what is the ambient temperature of transformer oil & winding?
how to select earthing conductor size of amy motor/panel etc.
OUR METER READER TAKE READING OF INDUSTRIAL CONSUMER.THEY ALWAYS ASK HOW TO INCREASE POWER FACTOR FROM 60% TO 99 % TO AVOID PENALTY OF POWER FACTOR.
Which level of the Transformer oil got dielectric strengh? And why?
how will reduce the voltage. if 12volt/250ma transformer toreduce 6 volt