Answer / kaja farkhan
Calibration is nothing but comparisonof an unknown standard
with an known standard or in other words it is known as
checking the output is proportional to the input or not.
Loop checking is nothing but the instrument installed in
the field must give the signal to the control room without
any break. First in this the continuity of the cable will
be checked from inst to JB in field side and from the JB to
control room.
Is This Answer Correct ? | 15 Yes | 3 No |
Answer / nagabalan
Loop check used to check the Field Instruments activity and
continuity from Field to DCS/PLC.
Field Instruments forced/simulated from filed and value
will be confirmed with DCS/PLC.
For Valves,value simulated from DCS/PLC and position will
be confirmed from the field.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / safeek_psna
I NEED TO SEND THE ANSWAR ABOUT INSTRUMENTAION
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / narenkumar1985
LOOP CHECKING MEANS CHECKING THE CABLE LOOP FROM THE INST TO
MARSHALING PANEL AND TO PLC. WHEN INST GIVING O/P SIGNAL TO
CONTROL ROOM-PLC CHECKING WHETHER THE SIGNAL GOING TO
CORRECT PLC CHANNEL.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / goldknight3000
Calibration of an instrument is a comparison to a known
standard. Eg. if i need to calibrate a weighing scale, then
we need a known weight for comparison. A known standard
have to be certified by certfying body like NIST.
Loop check is a continuity test coming from/to field to
junction box and junction box to/from Control system.
Is This Answer Correct ? | 0 Yes | 2 No |
admittance level sensor meaning?
Tell me about PID Tuning and what is PID.
What is the IEC Standard for PLC I/O Terminal wiring Procedure?
Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.pls help me
what is the difference between sensor and tranducers?
what is INSTRUMENTATION ? specify..
What is cable size for intrenal wiring in DCS or PLC ,from any card to Terminal amd Why
in rotark mov in display err msg showing how to remove the error
How can I map a tank? Tank 15m h and 42m dia. we just fixed radar type lit. its reading shows over range. Now its required mapping ?
GIVE BRIEF DESCRIPTION ABOUT "DCS"
What FLOW METER generally used in Gas plant?
why the supply frequency used in America is 60Hz while that used in India is 50Hz?,