for a 5hp motor to operate from 100kva generator ,what size
of cable required in sqmm.
Answers were Sorted based on User's Feedback
Answer / deepak prabhu
5 Hp motor usually comes in 3 ph only.and DOL starter of 3 phase is also available. Cable size doesn't depends on KVA of generators. In 3ph, 5Hp=3.7KW. =11A. By cosidering factor of safety we can use 4.0 sq mm copper cable.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mohammad farman khan-abu dhabi
5HP Motor are use as single phase on D.O.L or Star/Delta
connection as 3 phase. If you use single phase then total
load is 3.7kw so we can use 6mm sq cable .if you use in y/D
connection the required to use 4cx6 sq mm cable.
Is This Answer Correct ? | 3 Yes | 2 No |
1. Why is the speed of shunt motor practically constant? 2. Why dc series motor use to start with heavy loads? 3. advantages & disadvantages of separately excited generator over self excited generator?
What are locations arc protection relay is fixed.
How much must be gape bitween 2 cable on cable tray?
WHAT ARE THE DATAS REQUIRED FOR PROTECTION AND METERING AND CONTROL AND LOGIC PREPARATION,HOW TO STUDY THE PROTECTION AND METERING?
When dc supply is fed to rotor of the alternator how it work?
What is the function of a turbo charger in a 1000kva DG set
What is difference between PVC cable & XLPE cable?
How one can check the charger of the mobile phone or any other charger .......... that is it working ? if , working is it delivering the required supply which is needed by the battery to charge properly ?
howmany insolaters needed in 66kv line
I have 1500KVA transformer ,How much Maximum KW Load is allowed?
15 Answers GKC Projects Limited GKCPL,
What is single break or Double break related to MCB?
Why alternators are designed at 0.8 pf lag?