11KW Delta motor is taking about 44Amps in star and goes
upto 70Amps in delta and trips OFF. The rated current is
26Amps. Application is for the blower. The motor takes ( no
load without coupling impller ) only 2.5A and 5Amps in star
& delta starter test.Need to know why its taking high
current.

Answers were Sorted based on User's Feedback



11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / rajendran

The motor takes very less current at no load than the
normal and when it is loaded it is taking the obnormal
currents even in delta operating mode....

it seems there must be a problem in the connections or in
the supply voltage of the mains or improper impeller
arrangement causing very high load.

probably there may be a problem in the connections only...
check the connections

Is This Answer Correct ?    9 Yes 4 No

11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / rajesh vallem

in blower applications before starting the motor damper
should be in close position.motor concerned it is ok
because no load current of the motor is ok.

Is This Answer Correct ?    5 Yes 0 No

11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / gunasekaran

u r not explain proberly it is due to inrust current for
star phase voltage=VL/sqrt3
for delta phase voltage=line voltage so it is taking more
current than star.normally at stating motor taking 5to 6
six times of the full load current i think nothing wrong u
can incress the relay setting and then start the motor

Is This Answer Correct ?    2 Yes 1 No

11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / boby

I think there is something wronng with imppller coupling
it alingment could be out. Because no load current of
motor is ok . So check the coupling alignment , motor
bearing and connection of input cable at main source.

Is This Answer Correct ?    1 Yes 1 No

11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / mohammed raffi

In Blower application, starting current will be more than
normal until it gets full speed due to dampers, hence
better idea to use OLR with starting current delay time and
running current delay time setting. so that while starting
time this OLR waits for some time delay even starting
current is more than normal and trip.

Is This Answer Correct ?    0 Yes 0 No

11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / tj

Following is the check seq. :

1 Check for correct DOR/Phase Seq, ensure termination is
correct n tight.
2 Check the relay for malfunction & its type if it is
thermal then increase setting a bit more than ratd amps &
chk, n if its micro proc based then adjust the setting
acording to motor starting curve.
3 Ensure that suction damper is at min. before starting.
4 Ensure the motor is correct according to fan torque.
5 Check for any abnormal sound or play from fan side.
6 Also check the cable, it should not be underrated, causing
higher potential drop at startup.

Hope the above helps you........

Is This Answer Correct ?    0 Yes 0 No

11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / anil bhatia

check rated current as you mentioned 26 amps
according to chart it should be 19/20 amps

Is This Answer Correct ?    0 Yes 1 No

11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / virendra

There could be two problems

1. the improper connection of the motor to starter mean the
phase sequence.

2. may be possible the one phase is missing & motor running
on 2 phasis means the single phasing phenomina

this is the only reason..........

Is This Answer Correct ?    1 Yes 3 No

11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / felixraj

check the coupling alignment,blower condition(bearing)

Is This Answer Correct ?    1 Yes 5 No

11KW Delta motor is taking about 44Amps in star and goes upto 70Amps in delta and trips OFF. The r..

Answer / suraj_ojha

I am agree with mr.rajendern there is some mistake is in
their control wiring of starter.

Is This Answer Correct ?    0 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

What happen when increese more than 50HZ fequincy.

5 Answers  


Explain what happens to the speed of a series motor as the load decreases

1 Answers  


How can we calculate the current if we have load in KVA and if the load in KW then what formula will be use for calculating the current. please give both the formula for calculating the current.

3 Answers  


How will you determine the rating of a motor for continuous duty variable load motor applications?

1 Answers  


what is the opencircuit tes &short circuit test in transformers ,why you need this test, in poen your connecting which votmeter why?

1 Answers  






What is the difference between lubricating oil and insulating Oil?

4 Answers   Orchid,


how many units (kwh) are there if in one MW?

5 Answers  


what is the easiest method of short circuit current calculation ? pls. derive with a mathematical example in real life application.

0 Answers   Mepax, NEPCO,


WE HAVE THE DC RECTIFIER 1500A, INPUT VOLTAGE IS 3 PHASE. HOW TO CALICULATE THE LOAD? 3 PHASE SIDE EITHER dC SIDE. PLEASE SUGGEST ME

0 Answers  


Briefly describe means used by electricity suppliers to influence the flow of active and reactive power in power networks (one for each type)?

0 Answers  


Why use in ht motore

0 Answers   ACB Group,


why the protection turbo generators is most complex?

0 Answers   Infres, L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)