why anti pumping relay is not given to tripping coil of the
breaker? why only to closing coil?
Answers were Sorted based on User's Feedback
Answer / karna
Actually in Breakers Closing coil and Trip coil are
operated on Pulse command (i.e just initaion is enough,
continous supply not required). Anitpuming Means once the
breaker is colsed ,again if anyone ( Auto Command, Through
TNC switch ) can close it will not close because in closing
circuit Antipuming NC will be in series, Once the breaker
close means antipuming will activate unitll trip command
given by us.
Tripping coil plays major role in Circuit brakers, because
if any faults ( i.e O/L, E/L, short Circuit etc..)occur
breakers has to tirp. For trip we can do manaully at any
time.
Is This Answer Correct ? | 2 Yes | 0 No |
Closing is on command and tripping is either on command or
auto .You are testing the circuit by closing the CB using
the control switch
Is This Answer Correct ? | 0 Yes | 0 No |
3ph line voltage 220v, how can run a 220v single ph motor or Light?
what is the surge arrestor?how it operates?what is the range for it?
what will happen if the prime mover on the field excitation of the on-coming generator fails?Explain.
0 Answers Ahsanullah University of Science and Technology,
Why does increasing the magnetic flux in the main field of a d.c motor cause the armature current to reduce??
i want to know is it possible to generate usefull power by coupling generator with motor & supply gives to motor by battery source then generator generates power. remove the battery source given to the motor & feed the supply from some of the generated power supply to the motor & motor runs continously. generator generate power contnously.is it possible ?
The synchronous machine excitation system explain
if field breaker of generator is closed prior to its rated speed on a power generating unit. what will be the effect on generator, unit transformer and starting transformer.
What are the main Electrical IS rules?
how to use single phase supply for a three phase equipement.
what diferent amoung three phase supply?
There are a trformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate