Can CT Secondary left open circuited and why(reason)?
Answers were Sorted based on User's Feedback
Answer / jayakumar.k
CT Secondary should never let open condition. Since there
is no opposing flux in secondary circuit Primary flux will
develop enormously high that would cause bursting of CT and
also damage to the person who is working with it.( Remember
induction principle)
Is This Answer Correct ? | 26 Yes | 0 No |
Answer / raul
absolutely NOT bcoz during normal operating conditions, the
primary and secondary current are equal and opposite to
each other.........so the mmf of both primary and secondary
are in direct opposition........but secondary current is a
bit lesser than d primary current and this difference is
utilised in magnetising the core.......but if the secondary
is left opened then there will be no demagnetising mmf left
and excessive flux will b generated in the core and due to
this enourmous amount of voltage will b produced in the
secondary which is very harmful for life and CT also. also
there will be a loss of accuracy in future due to residual
flux left in the core.
Is This Answer Correct ? | 5 Yes | 2 No |
Answer / muhammad nazim
A CT is basically a step-up transformer(from voltage point
of view).In the case of 400/1 A CT the primary turn is 1
(say the busbar)and the secondary turns is 400.How much
will be the primary voltage drop?? it will be in millivolts
for a busbar.So this millivolts multiplied by 400 will
cause just around a few volts (say 3 to 10V) for an open
secondary.But i have read that the secondary voltage will
reach a few kilovolts for a 400/1A CT at full load
conditions.My question is how it will reach a few kilovolts
and damage the CT on open secondary condition?As we have
seen above the max voltage wil be just in few volts.So
please someone
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / bharat sharma
Let us assume we have 600 V and 200 A on primary side of the
CT. Ct ratio is 200:1 In that case Secondary voltage would
be (600V x 200A)/1A = 120000 V. Would you like to leave
120000 V open circuit irrespective of current capacity of
secondary circuit?
Is This Answer Correct ? | 8 Yes | 10 No |
what is the difference between Resin Cast CT and Oil cooled CT?
why hv winding is not placed near to transformer core
What are the various types of rotor used in the alternators?
hi, in the event earth grounding is not available in a project, is there any other way to make the elcb work? fyi, i have an instant water heater (6.5kw) installed, however if there is grounding in the heating element inside the heater assembly, i will get grounded. thank you in advance to those who will answer my question.
How to design the NGR Resistance
what are the functions of fuse ?
What is sequence network? Discuss all three types of sequence network.
what is the clear formula to calculate cable size for a load
What is the direction of current flow in ct secondary...means if the current is flowing from P1 to P2 then what will be the direction of current flow in ct secondaryw
Please explain me abt PQ diagaram in the power sector.
plz explain the snubber circuit unit
Difference between split ac and cassete ac?