How to protect the water pump by no load running.
Answers were Sorted based on User's Feedback
Answer / prakash
If your concerns with domestic water pump dry run control,
then you can use a floating switch at level point that can
be connected to series with DOL starter if already installed.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jimmy
Just put level switch NC contact in series with overload
contacts in the Starter Circuit.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / kamal
By using under current relay , setting is no load current,
below this level it trip.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / parth belani
We can protect a pump from no load running by using a
minimum recirculation line. This line connects outlet with
the main tank or the inlet. so there will always be some
minimum flow through the pump.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sandip paithankar
put a moisture sensor in land which need to wet on starting and ending point of it.then give to transistor then micro controller do if else program and understand the condition of land it may wet or dry.then give command to relay to operate the water pump
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ks
by using the level transmitter and with out plc with some
no nc additional elements in the contactor it is possible
to control.
Is This Answer Correct ? | 0 Yes | 3 No |
Answer / subrat.das1985
i think we can over come from this problem by using proximity sensor.or by using timer .
Is This Answer Correct ? | 0 Yes | 3 No |
Which type of DG need Netral Earthing?
Please provide me detail cable voltage drop calculation
Why diesel tank kept in 990 ltrs
why crgo core is used in transformers?
why the measure taken in multiplication factor of 11for voltage like.. 110V,220V,440V,1.1KV,6.6KV,11KV,33KV,66KV,110KV,132KV,220KV
what is the difference between LT and HT power supply?
26 Answers Center One Mall, Central University, JSW, Siemens, Suzlon,
PLease anyone can tell me CTUM-15 specification?
How to calculate the breaking capacity(like 15ka,20ka) of Circuit breaker (MCB,MCCB,ACB)
9 Answers Career Excellent Sdn Bhd, Neona, Northern Max Engineering, Sps Renewables, Terasaki, UEM,
what are the main hormonics in ac?
VCB in closed position during opertion if vaccume break then what will happend? it has any protection ?
how does a liquid starter reduce the starting currents?
for a 5hp motor to operate from 100kva generator ,what size of cable required in sqmm.
2 Answers DSC, Indraprastha Gas Limited IGL, UltraTech,