what happen if transformer neutral not earth
Answers were Sorted based on User's Feedback
Answer / shariff
Trf will fail as the un-balanced current will enter in the main windings.
Is This Answer Correct ? | 6 Yes | 1 No |
Neutral is grounded to protect against earth faults and to eliminate transient voltages. If not earthed we would never know that a conductor has fallen down and during this if another conductor falls down ,the fault current will be 73.2 % more.With one conductor fallen on ground the voltage between healthy conductor and the ground will be 1.732 times the normal
Is This Answer Correct ? | 1 Yes | 2 No |