1 no. 22 kV feeder is taken from state electricity board.
350 MVA is the S.C. MVA.
now i am feeding this feeder to HT Panel having 2 outgoings
which further supply to 2 Transformers.
Can you please suggest me the type & rating of cables
are 3 of these cables same?
or they are different?
please help...............
Answers were Sorted based on User's Feedback
Answer / latesh patel
2 Runs of 300 Sq.mm. cable will be sufficient for the 22KV
side incoming and the same will at outgoin side
irrespective of load connectd till the voltage level
changes to till lower 11 kv or 415 means txr should come in
picture...