what do you mean by switchgears?
Answer Posted / hjthegreat
switchgear is electrical disconnect switches combine with
fuses or circuit breakers.
not all disconnect switches call switchgear, only the big
one which commonly drive by motor
switchgear is used to control, protect automatically or
isolate electrical equipment manually.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
what will happen if ac and dc supplies given
How can I model an open-delta ground transformer for a network supplied by 4 unit GTG and power transformer in ETAP?
Advantages of using generator circuit breaker (GCB) scheme in a power station ?
how to interlock 3 incomer-ACB,1 buscoupler ACB,... pls answer this question and if possible send me the ckt diagram..haifriends2910@gmail.com
What is a Phase shift meter? Where can I get one?
why EMF IS INDUCED IN A CONDUCTOR WHEN FLUX LINKING WITH IT CHANGES ACCORDING TO FARADAYS LAW.
some time we open engine breaker 8.0 MW load but plant not trip. and another time engine open 4.0 MW load engine trip why? individually engine breaker open & individually emergency stop why difference?
how to calculate the change over time for star delta starter for different KW motor?
How to reduce the static electricity producing in solvent room? By P.D.Patil BioCon
How to do maintenance of transformer feeder.
why does the magnetic balance tests at transformer?
how to select electrical equipment such as fuse,dg,transformer,motor,msb,wire,cable as per the connecting load..please mention any books to design,take licence
is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.
How to Calculate Current Rating of SDFU (Switch Disconnector Fuse unit) for Protectionof Capacitor Bank connected to Busbar of 800Amp,in LV side of 11/0.433KV, 250KVA Transformer?
Did RMU have ct and pt ?